I'm curious, since it seems like all the items you post seem to be "grey market" or non-NA items, it seems like the strike in this case, a reader in another case, and a pushbutton in a third...with a lot of unconventional installation methods, as viewed from within the trade (I've installed/serviced in NA and the EU).
In my particular case, I'm going to point out a few things. Myself or coworkers work with strikes, locks, mags, handsets and similar on an almost daily basis, with one site totalling over 2k access controlled doors, not to mention the others we deal with (and are taking over as we speak).
1. Gatchel is correct regarding cable size. It's not something that can be guessed and values plugged into a formula and factor in an arbitrary voltage drop and loss factor...items won't work or won't work properly. Every hardware manufacturer has a chart, either on the instructions or somewhere else that is conspicous with a minimum AWG, distance and voltage that is being supplied. Those charts take into consideration a lot of factors, like I alluded to, inrush is a huge one.
In the case of something like a Von Duprin or some electrified handsets, they may only draw 500 mA, however the inrush current can be up to 20A, so the cabling size of 18 or 22, which meets the continous load, would be a nice "fuse" when the inrush current comes to play.
2. I cited a specific manufacturer and model of strike that needs constant power and a trigger cable. It draws 40 mA in "standby" and up to 300 mA while "unlocking" and from experience, they sometimes draw more if there's a load or the motorized part stalls while unlocking. There are a handful of similar models by almost all the common manufacturers that operate in some similar manner, pushing back the deadlatch/bolt arrangement.
3. If monitoring the bolt via a strike you need to plan for additional cabling, splicing as well as some strikes vary if "options" exist for the strike itself. The monitoring portion is only intended for the presence of the bolt, not if the door is closed or open, a DSM contact is always the correct way to determine this. As Gatchel alluded to, if the strike is going to be held unlocked for any length of time, plan on the strike heating up pretty well, some manufacturers provide diode and resistor packs to help with the heating and voltage loading to the solenoid.
4. Voltage drop is never really desired to be more than 10%-15% variance over the listed rating of the lock, which is what most lock manufacturers will consider normal operating conditions.