ELK M1 and System Sensor wiring

I need some additional assistance on this subject.  I have purchased 10 SS 2WTA-B smokes, the RRS-MOD and 2W-MOD2.  I need clarification on the correct connections to the ELK panel.  I have attached the link to the diagram (Figure 2) that I believe is correct to show a trouble zone.  Can someone tell me for sure where the other wires connect to panel?  Also how do I jumper zone(fire) 16?  Thanks!
 
 
 
 
https://www.systemsensor.com/en-us/Documents/2W-MOD2_RRS-MOD_modulewiring_techbulletin.pdf
 
AUX Power Resettable would be SAUX
 
4 Wire IDC would be your fire zone. e.g. Zone 16 JP1 jumpered for Normal. Or use any other zone.
 
MAINT/FREEZE IDC would be any zone input, configured as the trouble zone.
 
AUX Power would be VAUX
 
Bell/Alarm Circuit would be a relay output (e.g. OUT3) that you turn on via a rule when the panel goes into the fire alarm state.
Connect the COM contact of OUT3 to +VAUX and the NO contact to T+ on the RSS-MOD.
 
WHENEVER ANY FIRE ALARM TURNS ON
  THEN TURN OUTPUT 003 ON
 
WHENEVER ANY FIRE ALARM CUTS OFF
  THEN TURN OUTPUT 003 OFF
 
 
You might be able to use one of the M1's voltage outputs rather than OUT3, but since I'm not sure of the trigger current requirement of the RSS-MOD, OUT3 is a sure-to-work way to do it.
 