I'm a little confused. If you have 2 Keypads and you have them on branch #1 (homerun)each keypad should have a terminating jumper on it but should a jumper be moved on the data bus hub?  



#2 BraveSirRobbin

BraveSirRobbin

    Cocoonut

  • Moderators
  • PipPipPipPip
  • 7401 posts

Posted 26 May 2018 - 11:37 AM

Not exactly sure what your setup is, but I think it is second example from the manual (see attached screen shot).

 

Attached File  M1dbhr_Screen_Shjot.jpg   251.68K   7 downloads

 

In that case you would terminate each keypad, but not the one on the DBHR


Edited by BraveSirRobbin, 26 May 2018 - 11:40 AM.


#3 Mridixon

Mridixon

    Cocooner

  • Registered
  • PipPip
  • 28 posts

Posted 26 May 2018 - 12:22 PM

     Reading a little bit more I see that my jumpers were set correctly and the hookup was correct. The issue was the keypad enrollment process and having 2 keypads with the same address. Thanks for the help!   