That is sort of what I had suspected...not doable with one of the Elk power supplies.The M1 input is 16.5 volts AC. Most of the ELK power products are 6, 12, or 24 volts DC. I would venture a guess that the CPU requires at least a 16.5 volt AC input source where it is converted to what the board needs for basic operation.
That is sort of what I had suspected...not doable with one of the Elk power supplies.
Pays to be the chief engineerIn reality you can power the M1 from a separate DC power supply.
In reality you can power the M1 from a separate DC power supply. Run 13 to 14 volts DC into the battery leads. Run a +13 volt wire from the +Battery input to one of the AC inputs so that the M1 will startup when the power switch is turned on.
I suggest using at least a 2 amp or larger power supply.
Pays to be the chief engineerIn reality you can power the M1 from a separate DC power supply.. So you lose a wall wart, but you gain a separate plug in power supply and either a UPS or a backup battery in case of power failure. Not sure it's worth it.
In reality you can power the M1 from a separate DC power supply. Run 13 to 14 volts DC into the battery leads. Run a +13 volt wire from the +Battery input to one of the AC inputs so that the M1 will startup when the power switch is turned on.
I suggest using at least a 2 amp or larger power supply.
Don't you need a diode in there someplace to prevent the M1 battery charging circuit from backfeeding into the external DC supply?
wont this cause the system to throw an AC falt?
Burglar alarm systems are normally wired following the NEC code article 725 (commonly called power limited circuits). Most burglar alarm system fall under article 725 section III (Class 2 and Class 3 circuits). These sections assume that the system is powered from a power supply which inherently limits the power output.
Look at your Elk "wall wart ". It has a label on it as follows: "Class 2 not wet, Class 3 wet". This is a requirement for a class 2 supply which means it essentially limits the power supply output to 8 amps.
To use article 725 wiring methods, your power supply must be Class 2 power limited. Using anything other than this would require other wiring methods covered in other articles. However, most alarms systems are installed using article 725 wiring and methods. Most burglar alarm wire is labeled CL2, CM or CL2/CM. If you use this wire you must follow article 725 and must have a power limited supply.
Just so you know.