/Trouble Shooting the ELK M1 data bus
1. Make sure the RS-485 data bus is properly terminated. You should have the terminating jumpers at the extreme ends of the data bus.
Example 1: Control and 1 keypad. Terminating resistor on the control and on the keypad.
Example 2: Control and two keypads with the keypads at the extreme ends of the data bus. Terminating resistor on each keypad. NO terminating resistor on the control.
2. Measure the bus resistance. Turn off all the power to the control with the ON/OFF switch. Using a Voltmeter set to the Ohms scale measure the resistance of the data bus across the A & B data terminals on the control. You should read 65 ohms +/- 10 ohms. If you read greater than 75 ohms, you do not have one of the terminating resistors in place. If you read less than 55 ohms, you have too many terminating resistors in place.
3. Set a unique address for each Keypad. All keypads come from the factory set to keypad address 1. Keypad 1 is always enrolled into the M1. You must set the address on any additional keypads.
Hold the "*" and F5 key for approximately 5 seconds or until the setup screen appears. Press the F1 key for address setup. Use the UP and DOWN keys to set the address you want. Press the EXIT key twice to get out of the setup mode.
Note: You can calibrate the temperature sensor on the keypad by pressing the F2 key and using the UP and DOWN keys to display the desired temperature.
4. Press the ELK key, then 9 key. Enter the Installer Code (Factory default 172839). You should now be at menu 1 which enrolls and unenrolls all bus devices. Press the RIGHT arrow key. The keypad will momentarily lose communication while the M1 searchs all possible devices on the data bus. When the keypad LCD display returns, press the RIGHT arrow key to review all the devices that was found on the data bus. Make sure they have all been found. If not, try the enrollment again by pressing the ELK key to back up a menu then RIGHT arrow again.
5. If a device has not been found, make sure that ALL Data A wire connections connect to Data A on all bus devices and Data B connects to Data B on all bus devices. If any are swapped, the device will not work right.
6. Monitor the data bus errors. Press the ELK key then the 8 key. Press the RIGHT arrow key, enter a master code or Installer code. Press 6, for system diagnostics, then RIGHT arrow key. The keypad will now be displaying Data Bus Errors. If you can see the data bus errors counting up, there is still a bus problem. Note: It is normal to have an occasional data bus error.
Caddx Transmitter Enrollment
The above data bus enrollment procedure does not enroll Caddx/GE Receivers, NX-408e, NX-416e, or NX-448e. If you are having problems enrolling the transmitters from the keypad, I have found that defaulting the wireless receiver module from Installer Global 45 programming generally solves the problem. After defaulting the Wireless, re-install all the transmitters. You should get a beep out of a speaker connected to Output 1 when the transmitter enrolls. Remember you can not enroll more than one transmitter per zone.
Look for the Red LED on the Caddx receiver to be blinking. If not, check your wiring.
Hope some of this will help. If you are still having a problem, contact ELK Technical at 800-797-9355.
Happy M1'ing.
David Steele
Chief Engineer
ELK Products, Inc.