if you have selected normally closed zone definition in the M1, then do not use the EOL resistor. Connect the PIR contacts directly to the M1 Control zone inputs or in series with any other switch or PIR on the same zone. The zone status should show shorted, 0 volts when everything is OK and open, 12-13 volts when the PIR is violated.