Zone Definition 23 Problem

rfdesq

Senior Member
Here is my setup:

One zone set to Definition 23 Police Notification Audible. It is connected to a Visonic wireless panic button. EOL resistor setting. The Visonic is wired for normally closed with a 2200 ohm resistor. There is about 7 volts present at the panel when not pressing the panic. When I press the panic the zone goes to about 13 volts. When I walk test the zone and press the panic, the interior speaker yells "panic, panic, panic", as I have programmed.

Here is my problem:

When I press the panic button, not in walk test mode, either from an armed or a disarmed state, instead of going into audible police notification with interior speaker yelling at me, I get a police trouble on the zone. I then have to enter a user code to clear the beeping. TIA.
 
Police Panic inputs need a short to activate the Police Alarm when in the End of line resistor mode. A circuit open triggers a police trouble. The normally open or normally closed zone input mode will not trigger a police trouble. It sounds like the receiver input is a normally closed output and opens upon triggering the panic button.
 
As always, you are correct. I have the NC output terminated with the EOL resistor. So, I need to rewire so the zone sees the EOL resistor and when the panic button is pressed it shorts the circuit. Correct?
 
I drew it out on the Visonic wiring diagram and it looks just as you describe it. Thanks for being here with all the right anwers.
 
Spanky,

I rewired the zone and now it works. Another question/problem, this zone definition does not allow for the XX second output 2 delay that other zones allow. Is this another hidden feature/quirk that is not in the installation manual?
 
The delay before alarm time setting in Globals only works with burglar defined zone types. You will need to write some Rules to delay output 2 on a Police defined zone definition 23.


Program the Police cutoff time to 1 second. This prevents Output 1 & 2 from coming on.

Write a Rule to turn on Output 1 alarm upon police activation for the amount of time to run Output 1.
Write a Rule to turn on an unused output for your time delay say 20 seconds.
Write a Rule to turn on Output 2 when the unused output cuts off for a time delay.

The 1 second Police cutoff time will not allow Output 1 or 2 to come on, but will activate the Police Alarm on the keypad and trigger the communicator. These Rules will control the outputs.

Example Rules:
WHENEVER ANY POLICE ALARM, ANY AREA TURNS ON
THEN TURN Output 001 (Out 1) ON FOR 10 MINS
THEN TURN Output 100 ON FOR 20 SECS //delays output 2 from coming on immediately
WHENEVER Output 100 STATE IS TURNED OFF
THEN TURN Output 002 (Out 2) ON FOR 9 MINS, 40 SECS
WHENEVER Area 1 (Area 1) ARM STATE BECOMES DISARMED
THEN TURN Output 001 (Out 1) OFF
THEN TURN Output 002 (Out 2) OFF
THEN TURN Output 100 OFF
 