Zone Types

heffneil

Active Member
Hey guys - I am a former Omnipro guy moved to ElkM1 and for some reason I appear brain dead. I have 2 CO detectors from the same manufacturer installed. One is new and I looked up the wiring and had it all wrong. I have since fixed it but it has a alarm relay type jumper. I couldn't get the zone to work unless I removed the jumper to make it NC (normally closed). The problem is that I removed the same jumper on the other previously installed unit and it immediately becomes violated. Not sure what is going on with this and the only difference is that the previously installed unit is terminated to the main panel. the CO sensor is a macurco CM-E1

 
Do you have the two CO detectors wired as a daisy chain on one zone?

I'm not sure what jumper you are referring to. Is this a jumper on the CM-E1, perhaps in place of the EOL resistor?

[Edit]: Ok, I figured out which jumper you are referring to: J2.

How do you have the zone defined (zone def and zone type)? Do you have an EOL resistor installed?
 
Last edited:
So they are on separate zones. There is a jumper on the sensor on how to behave. I tried to link the page to show that it has its own end-of-line resistor wiring leads (its very different) that I don't know if it is inline or parallel. Either way it's behaving like it is safe on both zones - even though one has the jumper and the other doesn't
 
Ok. What are you using for the zone def and zone type for each of the zones? Do you have EOL resistors installed on either of the detectors?
 
I've been puzzling over the symptoms you describe and I think I can explain what is causing some of your problems, but perhaps not all of them.

The CM-E1 is works in a manner like a 4-wire smoke detector. The EOL resistor is in series with the normally closed trouble relay and is in parallel with the normally open alarm relay in the CM-E1. This allows multiple detectors to be daisy chained together. In normal operation, the alarm relay would be open and the M1 would see the 2200 ohm EOL resistance, making the zone voltage about 6 volts or so. When the detector goes into alarm mode, the relay closes and shorts the EOL resistor, dropping the zone voltage to 0 Volts, and the M1 goes into alarm mode.

If the detector has a trouble condition, the trouble relay opens, creating an open on the zone loop, and the M1 zone voltage goes to 12V and the M1 senses the trouble condition.

When you specified the zone type of 0 (EOL/wireless), the M1 expects to see the 2200 ohm EOL resistance and about 6V on the zone during normal operation. When you removed the J2 jumper, I think you caused the CM-E1 alarm relay to be closed during normal operation, shorting out the EOL resistor. This should have caused an alarm condition at the M1, which is what you say you saw with the second CM-E1 that you installed.

What I can't explain is why this didn't also happen with the first CM-E1. I think you say removing the jumper made it work. I'm not sure how that could be, unless you have some high resistance in your loop wiring. I would measure the voltage at the M1 terminals on this zone and see what it is when the jumper is removed. That should give us a clue to what is going on.

I think the proper zone def and type for these zones is Zone Def 17 (CO 24 Hour) and Zone Type 5 (Fire, 4-Wire Smoke Detector).

You should install jumper J2 on both detectors.
 