Newer sensors are digital but older ones were not.
If you haven't discovered it already, each zone is a volt meter. When you use a EOL resistor, the zone is measuring the voltage across that zone to determine if the zone is faulted or open or closed. If you look in PC Access you see a number representation for each zone from 0 to 255. THAT is the voltage it is seeing across the zone terminals.
HAI certainly wouldn't recommend using the zones to measure voltage, but guess what, they do it with their temp sensors. In fact their older temp sensor is nothing more than a temp to voltage sensor. Take a volt meter and measure from ground to sensor output and you will see a voltage representing the temperature. Its not rocket science. Zones are also pretty protected against surges and such because long wires can experience these things. If you are careful and don't exceed 5 V in a zone, you shouldn't hurt it.
BobS0327 said:
This is also evident in the Omni Link II protocol document where input temperatures are mapped from 0 to 255. 0 being -40 F to 255 being 189.5 F.
PM me if you should need a copy of the Omni Protocol II document.
The fact that HAI tells you the temp conversion for 0 to 255 certainly does NOT indicate that the signals are digital. In fact, just the opposite. the analog-to-digital converts HAI uses on each zone are 8-bit, producing a number from 0 to 255, just like in PC Access, you see values for each zone from 0 to 255. I believe it uses a 12V reference where a 1 = 12/255 = 0.047 volts, 2 = 2*(12/255) = 0.094 volts, 3 = 3*(12/255) = 0.141 volts, etc
So to test for 3V, your number is 64, then check the docs to see what "temperature" 64 is.