I need to add some modules but will run past the 550 ma limit pretty easily.
Most of the modules draw their power off the keybus, not the aux terminals.
My current installation includes
Keypad 5500Z = 85 ma
Keypad 5500Z = 85 ma
Keypad 5516Z = 90 ma
IT100 Interface = 90 ma
5108 expansion = 35 ma
That's 385 ma on the keybus so far.
Two motion sensors at 17.5 ma each (in alarm mode).
So the motion sensors are the only things I have that don't draw power off the keybus.
I'm about to ad
Envisalink 4 = 60 ma
5700 Fire = 150 ma
So my question is, how can I add power to the keybus? The only thing I have that's not taking power off the keybus is a mere 35 ma (motion sensors).
If I add a 5204 or 5200, will that add power directly to the kebus? I'm guessing not as the 5204 has a 20 ma draw itself from the 550 ma 5010 even though the 5204 has it's on power supply.
How do people add 8 or more keypads or is the 1832 just not able to scale up like that?
Keypad 5500Z = 85 ma
Most of the modules draw their power off the keybus, not the aux terminals.
My current installation includes
Keypad 5500Z = 85 ma
Keypad 5500Z = 85 ma
Keypad 5516Z = 90 ma
IT100 Interface = 90 ma
5108 expansion = 35 ma
That's 385 ma on the keybus so far.
Two motion sensors at 17.5 ma each (in alarm mode).
So the motion sensors are the only things I have that don't draw power off the keybus.
I'm about to ad
Envisalink 4 = 60 ma
5700 Fire = 150 ma
So my question is, how can I add power to the keybus? The only thing I have that's not taking power off the keybus is a mere 35 ma (motion sensors).
If I add a 5204 or 5200, will that add power directly to the kebus? I'm guessing not as the 5204 has a 20 ma draw itself from the 550 ma 5010 even though the 5204 has it's on power supply.
How do people add 8 or more keypads or is the 1832 just not able to scale up like that?
Keypad 5500Z = 85 ma