Oh boy. The AHJ would have a field day with Ano's install.
Sprinkler system is thermal and not activated electronically, unless it is a dry or preaction. A flood detector would not be a suitable device (or listed) for fire alarm service. The systems, as separately installed would be compliant, however once you start linking them for monitoring and reporting is where the issues lie. I'd hopefully assume the unit needs to see a sample of a temp-3 sounder before sending it's signal to the host panel.
The inherent issue is the 120VAC smoke alarms (NOT detectors, very specific difference) are a compliant system for code. The RF device and link to a listed control panel would technically be compliant, assuming the AHJ allows the ETL listing on the device and not UL/FM to apply specifically to the unit as connected to the FACP and the communication unit does meet the UL listing requirements in the standard. The inherent issue is when you link 2 separately listed systems in a manner that has not been specifically addressed in NFPA or the IRC, which most state statutes are dervied from.
How about this: Where's the supervision portion performed on the host system? Where's the interconnection supervision? Where's the annunciation of trouble? What happens should the unit not "hear" the alarm? Is one to assume that the boilerplate "test system weekly" requirement is going to apply in this case and device?