I'm not an expert on the DSC 1832, but here is what I see from digging through the manual.
You need to add up the maximum current requirements of all the devices that draw power from the Keybus, PGM and AUX outputs and compare that to the maximum output capability of the panel. This would include keypads, expansion modules like the PC5108, and things like smokes and PIR detectors that are drawing power from the AUX power terminals.
There is a table in the DSC 1832 manual that gives the current requirements for the various supported DSC devices. You will have to consult the manuals for smokes, PIRs, etc separately to get their current requirements.
One section in the DSC manual says that the AUX+ output is capable of providing 700 mA. Above that, you need an additional power supply. A good rule of thumb is to not push it right up to the maximum, but to stay below 80%, which would be 560 mA.
Another note in the manual says "current draw from Keypads, PGM Outputs and Aux circuits must not exceed 550 mA." I'm not sure why it specifies 550 mA when elsewhere the manual says 700 mA, unless they are derating things for you according to the 80% rule.
For sirens and screamers, you need to add them up separately, as the BELL outputs have a separate 700mA maximum current limit.