I am looking at installing these heat sensors, assuming they will work with the Elk. It appears that they support 6-125 VAC, which doesn't make sense to me, so I am hoping an electrician can pipe in here. Are these essentially the equivilent to a 2-wire smoke?
http://www.systemsensor.com/html/cd.html?UniqueID=107
Heat sensors are unpowered devices which have a dry contact only in them. In normal condition the contacts are open, and in alarm condition the contacts are closed. This is reverse from a standard burglary device, where the contacts open on alarm.
For this reason, and to meet the codes involved, heat sensors must be placed on their own zone and have an EOL resistor in the circuit. In the Elk, define the zone as a definition 10, "fire alarm", with type 5 "Fire/4-wire smoke". You can more than one heat sensor on a zone, just follow the manufacturers instructions to do so.