ccmichaelson said:
@RAL: Thank you - you are seriously the most helpful person I've meet on this forum (specifically answering questions rather than rambling on about off-topic items)
Last question (I hope), what battery(s) would you recommend I purchase? According to the ELK draw spreadsheet, I'm going to use approx. 2.2 AMPS (although planning for a little growth so I'd say 3 AMPS. I plan to put most of the devices requiring power on the power supply (rather than ELK panel).
My ELK M1 Gold kit came with a 12V 8AH battery. I looked at Altronix's website and the only ones that would fit inside the can are the BT124 and BT126. Perhaps I purchase two of them or I could get the much larger one and install it outside the can.
What size battery you need takes a bit of calculation.
You want the aux power supply to have enough battery capacity so that it will last longer than the M1's battery. The reason is that if the aux supply battery runs down first, the power loss may cause problems for the M1 which will still be running, say if you have keypads or input expanders connected to the aux supply. Or any devices that will indicate a fault when they loose power.
A simple approach to the calculation would be to take the total current draw on the M1's battery, and divide that into the size of the battery in Amp-hours. For an example, if the Elk current draw spread sheet says that the total current draw is 0.8A, and you have an 8 Ah battery, then it should last about 10 hours.
Next, you need to add up the total current draw on your aux supply. If it is 2.2 Amps, and you want it to last at least 10 hours, then you need a battery that is at least 22 Ah (2.2A x 10 hours).
You may be able to get additional time out of the battery on either the M1 or the aux supply if you have devices that are normally in standby mode but draw more power when they go active. I take the standby current into account when I estimate the battery time, but use the maximum current in calculating the total load that the supply may have to deliver.
So, if I have my strobe connected to the aux supply, and it draws 210 mA when active, I use the 210 mA in calculating the total load on the aux supply. But I subtract that out when estimating the battery run time, since the strobe isn't active except in an alarm condition.
You should be able to fit two 1290 batteries (9 Ah each) in the AL600 can. You would wire them in parallel, and that will give you 18 Ah capacity, which seems like it would get you close to where you want to be. If you need larger batteries, then you'll need a separate enclosure for the batteries.
That said, going with larger batteries for the aux supply may not be the only solution. Larger batteries get more expensive. You may be able to down size the battery on the M1 a bit to the point where it balances properly with the aux batteries. So maybe a 7Ah battery would get you there. But don't go too small, or you may not have adequate run time. I wouldn't go below 4 hours and personally prefer to be higher than that.
I've had good experiences with Power Sonic batteries, which I've been buying from ecomelectronics on eBay.
http://www.ebay.com/itm/380884922880
Here's a good reference to the
battery sizes available from Power Sonic. Other manufacturers also make batteries in the same capacities and physical sizes.
One thing to watch out for is the battery terminal type when ordering. Some batteries are available with F1, F2 or NB terminals. So make sure you know which one you need. Though if you end up with the wrong one, there are adapters available.