I installed an new M1 panel along with 8 wired sensors and 42 wireless sensors (interlogix 319.5 ) most of the sensors are the new Tx-E201 window/door sensors. When I reboot the panel it takes about an hour to go through all the zones. It keeps showing that # zones are violated. After about an hour I get the ready to arm meassage.
This is the 3rd install I have done with an Elk-M1 panel and I do not remember any of them having this problem. I have checked and rechecked the wiring and termination. I installed two keypads and and the wireless receiver with the Elk M1DBH. Thinking that could be the problem I disconnected it and wired everything the old fashion way. Daisy chained the 2 keypads and terminated the last. Ran the wireless receiver on its own run and terminated it. No termination on the panel.
I am thinking I just may have a bad Elk-M1XRFEG.
Any help would be greatly appreciated!
Thanks
This is the 3rd install I have done with an Elk-M1 panel and I do not remember any of them having this problem. I have checked and rechecked the wiring and termination. I installed two keypads and and the wireless receiver with the Elk M1DBH. Thinking that could be the problem I disconnected it and wired everything the old fashion way. Daisy chained the 2 keypads and terminated the last. Ran the wireless receiver on its own run and terminated it. No termination on the panel.