I am migrating from an Ademco with a 2000 ohm EOL resistor on the fire zone to an Elk M1 with a 820 ohms (2-wire smoke on Zone 16).
The problem is that I cannot find the resistor, it's probably somewhere in a wall/ceiling.
Is there a way to make it work? I see the 4-wire smoke requires a 2200 ohms.
Can I add add a 200 ohms in series and use a regular zone (ignoring the power)?
Thanks for any help on this, my wife seems to be reluctant to me opening the walls