[snip]...Old wiring...[snip]
RC ------- Cooling Power -------------------------------------------------------------------- Red
R ----------Heating Power ------/
Y ----------Compressor contactor ----------------------------------------------------------- Yellow
C ----------Common wire from secondary side of cooling system transformer --------- Blue
O/B -------Changeover valve for heat pumps --------------------------------------------- Orange
G ----------Fan Relay ------------------------------------------------------------------------- Green
Aux -------Auxiliary heat relay -------------------------------------------------------------- White
Here is my guess:
Old Thermostat ----------------- 8870
RC and R ------------------- RH and RC
Y ------------------------ ???????
C ------------------------- C
O/B ------------------------ split wire to O and to B???????
G --------------------------- G
Aux ------------------------ W1??????
This is pretty general but it may help some other folks also: Disclaimer: the below terminals/colors are for the above poster's application! NOT ALL UNITS ARE THE SAME! Always consult the wiring diagram that is inside your heat pump air exchanger or the thermostat itself.
On a normal HVAC system, the Y's are for various COOL stages of the compressor; on a heat pump the first Y is for cooling AND heating. Remember the same compressor is used for both roles on a heat pump. Y -to- Y1
On a normal HVAC system, the W's are for various stages, different types, or speeds of HEAT (ie W1 may be gas, W2 is geothermal, etc); on a heat pump the first W terminal is always the Emerg./Aux Heat (also 'defrost', but you don't have to worry with this). Aux -to- W1
G is easy, Blower. G -to- G
The O/B: your existing thermo can go two ways: it either energizes for for cool or energized for heat. Your heat pump obviously only has one reversing valve: give it power for cool. FYI some heat pumps use two: this is why the 8870 splits it into two terminals. Anyways you likely need O -to- O. If the thermostat works in reverse (cools when it should be heating) then simply swith your Orange wire to B then.
On your old thermostat, was there a jumper between RC and R?
R -to- RC & RH
!!! For 8870 standalone operation you will need C (usually 'B') from the heatpump to C on the 8870. Also a jumper from RC/RH to R on the 8870. This is to provide power to the actual front panel thermostat electronics.
!!! For 8870 automated operation remove the above jumpers going to C and R. Your RS484 wiring will now provide power (from the Arpilare distro panel).
PLEASE verify this: I am researching the connection of an 8870 to my own heat pump and the above is very close to mine (terminals are a little different because it's a Trane unit).
A follow up on this if you do not mind. I have looked at the wiring for the floor that has a two stage heat pump. I am not sure of all of the specifics, but a first stage will start at a relatively low speed (and lower energy use) and if the difference in between the actual temperature and what you have is greater than a specific value, then the second stage will kick in.
That is how it works with the cooling and heating, but with the heating there are "emergency" electric heat strips also (a third stage?).
When I looked at the wiring for the floor with the two stage, there was only one wire added and it was placed in Y2. I assume from your above post that since Y is cooling (first stage), then Y2 is cooling (second stage).
There is no wire for W2, which I assume would be heating for some stage? If W1 is the "emergency" strips, then do I need a wire for W2? Or, since it is a heat pump, the wires on the Y side suffice for control of the compressor?
This may be all theoretical since I wired it up as you suggested (with the addition of the Y2 wire) and it seems to work fine.
It is strange but very cool and satisfying to control your HVAC system from 100 miles away. Now to find a practical purpose!
Thanks,
CT
The practical purpose would be that when you go away on vacation for 2 weeks and set your AC for 78 degrees to keep the cats comfortable not to come home and find the AC set for 65 degrees by your sister in-law who fed the cats for you