Basically, a relay with the coil associated with the AC line and the relay NO contacts connected to a zone configured as type 16 (non-alarm) or type 32 (power supervisory). Type 16 would be for rules use only. I assume that type 32 would give you trouble alerts to the monitoring station, which you may or may not want.
You can either use a 110VAC relay if you are comfortable with high voltage wiring. Or you can use a relay with the coil voltage matching a spare wall wart transformer you have.
Interesting didn't know about zone definition 32. My UPS's have NO and NC alarm relay terminals, so that will prob work great.
Power Supervisory 24 hr - For supervising an external power supply which provides alarm/trouble contacts. Wire
the power supply contacts to open the zone in a Low Battery event and short the zone in an AC Failure event.
This description makes it sound as of open and shorted are both abnormal conditions. How can that be? There is no mention of resistors for this zone type.
So if a zone type 32 is created, will that supersede what the Elk does natively regarding its main power input?