midon
To determine accuracy the DS2438 is a 10-Bit Analog to Digital converter. If you looked at the Analog to Digital Converter Guide you would see ten bits is "2 to the 10th" power or 1024. This means the "measured" voltage (ten volts max) has a bit accuracy of 10/1024 or .01 volts.
Let's not confuse resolution with accuracy! The resolution of the DS2438 is indeed 10mV (0.01V). The accuracy of the ADC is given as +/-75mV over the input range of 1.5 to 10.0V on the VAD input (per the spec sheet). NOTE: the circuit in the diagram uses the VDD input to measure the battery voltage. The VDD input accuracy is greater than the VAD input (50mV instead of 75mV but has a lower bottom threshold - 2.4V instead of 1.5).
Your accuracy is also affected by the tolerance of the resistors chosen. 1% resistors are extremely common these days, so they should not induce much of an error and, if chosen carefully, can have no effect on the accuracy.
Regardless of all this, the OP was looking for 0.1V accuracy, so the DS2438 is a reasonable fit for this.
Mitch