Should that only to bitwise operator or to all AND/OR/XOR?
Also, after change, if user just want to store a bit to a variable, they must add
NOP
if the bit was zero. Otherwise, it will be skipped.
In case the bit is changing and programmer does not know the bit value before hand, then it will need always add
NOP
to prevent skip next logic.
Maybe the better way is to add additional PLC command that can skip.
We can add more PLC commands, since that does not require using additional RAM.
Please let us know how many commands would be helpful and suggestion of their unique names.
Yes that is what he suggested.  Leave the bitwise commands alone and add:
TANDB
TORB
TXORB
TOR
TAND
TXOR
and make ZB or ZBIT a variable referencing the zero bit
CAI_Support said:
Thanks for your suggestion.  What the 'T' stand for?  just for easier to document.
This is what I meant.  Leave the current bitwise operations alone.  Add new ones.
TSTANDB
TSTORB
TSTXORB
or,
TANDB
TORB
TXORB
The "T" or "TST" stand for "test".  They would function the same as TSTEQ, TSTGT, etc.  where a true result executes the next line and a false result skips.
az1324 said:
Also, it would be potentially useful to have the zero bit as an operand
ANDB RAM1 RAM2
SET RAM3 ZB
Tell me if I am wrong, since I have never used the "logical AND", etc.
But, wouldn't this give you the same result
AND RAM1 RAM2 RAM3
Say you had RAM1=1 and RAM2=2.  ANDB would give 0.  AND would give 1.  ZB from ANDB would be 0.
Say you had RAM1=1 and RAM2=3.  ANDB would give 2.  AND would give 1.  ZB from ANDB would be 1.
So having ZB as a variable allows you to use the logical result of a bitwise function.  Can be useful.
Lou Apo said:
Let me think about this.  I would rather have it switch at the 15 minute mark.
Also, try deleting the middle line (ANDB RAM1 3).  I think the zero bit should not need to be set again.
CZ RESET                            * if neither flag set (zero bit 0), shuts off relays
ANDB RAM1 3                      * tests if either of above flags set, might not be needed, depends if "x10" changes 0 bit
CNZ RELAY                          * if either flag set (zero bit not 0), runs the relay sub
Hi,
I removed line ANDB RAM1 3 and the OP1 and OP2 are switching more or less 15min 15sec after the hour..
laodice said:
Hi,
OK, well then setting x10 devices does not affect the zero bit.  But this shouldn't have anything to do with the timing of the relays switching.  There is basically a 60 second timer that only lets the code that switches the relays run once per minute.  The timer starts when the unit first boots, so if you boot it 15 seconds after the minute, then it will stay on that schedule.
I think this will make it always run on the minute by adding 2 lines.
START
TSTLT CYEAR 2013             * waits for clock to bet set before proceeding
GOTO START
TSTNE CS 0              *** add this line
GOTO START          ***  add this line
SET RAM2 CTS
So, tell me if I am correct.
Logical AND, OR, XOR looks at a 0 as false and non-zero as true?  The result of any of the three would be either true or false (1 or 0) and that would be the only two possibilities for the result?
using the symbols
NZ for non-zero number (I assume this includes negative numbers)
Z for zero
Where you use the following format
operator RAM1 RAM2 RAM3
AND
results
RAM1=NZ RAM2=NZ RAM3 = 1
RAM1=Z   RAM2=Z   RAM3 = 1
RAM1=NZ RAM2=Z  RAM3 = 0
RAM1=Z  RAM2=NZ RAM3 = 0
OR
results
RAM1=Z RAM2=Z RAM3 = 0
RAM1=NZ RAM2=Z  RAM3 =1
RAM1=Z RAM2=NZ RAM3 = 1
XOR
results
RAM1=NZ RAM2=NZ RAM3 = 0
RAM1=NZ RAM2=Z RAM3 = 1
AND
results
Hi,
I tried to understand the codes and adapted them to:
-Check day and night  if the door is open (IP=0) and if so send an email and set OP3 high (siren) for about 45 sec: this works but not always between 21h and 22h
-Between 21h and 22h switch OP1 and OP2 on and off every 20 minutes: this works fine
-Between 22h and 23h switch on and of two X10 devices every 15 minutes this works but not restricted to this period
-IP8 controls the on and off of the whole system
START
            CALLSUB INIT_OUT
            SET RAM2 CTS
LOOP:
            TSTEQ CH 21
            CALLSUB RELAY
            TSTLE CH 20
            CALLSUB RESET
            TSTGE CH 22
            CALLSUB RESET
TSTLT CTS RAM2
GOTO LOOP
ADD RAM2 60 RAM2
SET RAM3 0
TSTGE CH 22
ORB RAM2 3 RAM3
TSTLT CH 23
ORB RAM1 2 RAM3
ANDB RAM3 3
CZ RESET1
ANDB RAM3 3
CNZ RELAY2
            CALLSUB CHECK_DIS
            TSTEQ VAR1 0
            CALLSUB DOORS
            TSTEQ OP3 1
            CALLSUB DISAB_ALM
            GOTO LOOP
            END
INIT_OUT:
            SET OP3 0
            SET OP1 0
            SET OP2 0
            SET VAR1 0
            RET
CHECK_DIS:
            TSTEQ IP8 0
            DELAY 50
            TSTEQ IP8 0
            SET VAR1 1
            TSTEQ IP8 1
            SET VAR1 0
            RET
DISAB_ALM:
            DELAY 60000
            SET OP3 0
            DELAY 100
            RET
DOORS:
            TSTEQ IP1[100] 0
            CALLSUB ALARM
            RET
ALARM:
            SET OP3 1
            EMAIL EM1
            RET
RELAY:
            DIV CTS 1200 RAM1
            ANDB RAM1 1
            BZ  RELAY1
            SET OP1 0
            DELAY 5000
            SET OP2 1
            RET
RELAY1:
            SET OP2 0
            DELAY 5000
            SET OP1 1
            RET
RESET:
            SET OP1 0
            SET OP2 0
            RET
RELAY2:
DIV CTS 900 RAM2
ANDB RAM2 1
BZ RELAY3
X10 2 0 0
X10 1 0 1
RET
RELAY3:
X10 2 0 1
X10 1 0 0
RET
RESET1:
X10 2 0 0
X10 1 0 0
RET
After looking at this a bit, I found some problems.  I really didn't follow the logic all the way to conclusion however.
Code:
START
CALLSUB INIT_OUT       $$$ this subroutine is not needed.  OP’s are 0 at boot unless you manually click “save state”
SET RAM2 CTS
LOOP:
TSTEQ CH 21
CALLSUB RELAY
TSTLE CH 20             $$$ change to TSTNE CH 21
CALLSUB RESET
TSTGE CH 22            $$$ delete
CALLSUB RESET      $$$ delete
TSTLT CTS RAM2
GOTO LOOP
ADD RAM2 60 RAM2
SET RAM3 0
TSTGE CH 22
ORB RAM2 3 RAM3         $$$RAM2 is CTS plus 60, did you mean ORB RAM3 1 RAM3?
TSTLT CH 23
ORB RAM1 2 RAM3         $$$ Did you mean ORB RAM3 2 RAM3?  All of this could be replaced with TSTEQ CH 22
ANDB RAM3 3
CZ RESET1
ANDB RAM3 3
CNZ RELAY2
CALLSUB CHECK_DIS
TSTEQ VAR1 0
CALLSUB DOORS
TSTEQ OP3 1
CALLSUB DISAB_ALM
GOTO LOOP
END
INIT_OUT:		Delete this.  Move set VAR1 0 up where the subroutine call is
SET OP3 0
SET OP1 0
SET OP2 0
SET VAR1 0
RET
CHECK_DIS:
TSTEQ IP8 0
DELAY 50
TSTEQ IP8 0
SET VAR1 1
TSTEQ IP8 1
SET VAR1 0
RET
DISAB_ALM:
DELAY 60000      $$$this is going to lock up the program for 60 seconds
SET OP3 0
DELAY 100
RET
DOORS:
TSTEQ IP1[100] 0
CALLSUB ALARM
RET
ALARM:
SET OP3 1
EMAIL EM1
RET
RELAY:
DIV CTS 1200 RAM1
ANDB RAM1 1
BZ  RELAY1
SET OP1 0
DELAY 5000       $$$ why do you need this, this locks up the program for 5 seconds
SET OP2 1
RET
RELAY1:
SET OP2 0
SET OP1 1
RET
RESET:
SET OP1 0
SET OP2 0
RET
RELAY2:
DIV CTS 900 RAM2
ANDB RAM2 1
BZ RELAY3
X10 2 0 0
X10 1 0 1
RET
RELAY3:
X10 2 0 1
X10 1 0 0
RET
RESET1:
X10 2 0 0
X10 1 0 0
RET
I used the DELAY code to keep the siren working for one minute.
Would it be better to use “SET OP3[60000] 1” instead of DELAY60000