Hello,
I have replaced the garage heat sensor from Edwards 284B-PL to System Sensor 5601P which I believe is a mechanical detector. Currently i have RRS-MOD with 2WTA-B on M1G. This statement from the manual is throwing me off. Am not suppose to use 5601P?
Also I plan to replace the RRS-MOD to COSMOD-2W and replace some 2WTA-B with COSMO-2W.
"When using the RRS-MOD with model 2WTA-B, do
not mix the 2WTA-B with other model smoke detectors
and dry contact closure devices, including
mechanical heat detectors, manual pull stations and
waterflow switches. Such mixing can cause a direct
short on the auxiliary power terminals, damaging
the control panel’s internal circuitry and/or damage
devices connected to the initiating device circuit."
I have replaced the garage heat sensor from Edwards 284B-PL to System Sensor 5601P which I believe is a mechanical detector. Currently i have RRS-MOD with 2WTA-B on M1G. This statement from the manual is throwing me off. Am not suppose to use 5601P?
Also I plan to replace the RRS-MOD to COSMOD-2W and replace some 2WTA-B with COSMO-2W.
"When using the RRS-MOD with model 2WTA-B, do
not mix the 2WTA-B with other model smoke detectors
and dry contact closure devices, including
mechanical heat detectors, manual pull stations and
waterflow switches. Such mixing can cause a direct
short on the auxiliary power terminals, damaging
the control panel’s internal circuitry and/or damage
devices connected to the initiating device circuit."