hult
Active Member
Yes, but the OP's application is >> 20 amps, so Smarthome's xrp 20-amp filters do not serve the purpose.
my 3kw inverter requires only a 20A breaker, as does the 4kw version (peaks at 17A)
I thought I'd read about a 4.7KW DC source somewhere in this thread for which the 5KW transformer I referenced would be suitable. Maybe it wasn't the OP.
Different breakers have different time-current curves and arc-breakng capabilities, but if the 120VAC power from your converter goes through a 20-amp circuit breaker UL-listed for residential service in US, the _continuous_ circuit current is supposed to be limited to ~2.4KW regardless of the manufacturer's specsmanship.
Is your converter UL listed for residential application? I found that there was/is a very large difference in price between non-listed units and UL-listed inverters
If not, whatever the manufacturer says/recommends/claims may not pertain to those installations where meeting National Electrical Code (if US) must be met in order to stay in conformance with locals rules and regs. That's the vast majority of the population of the US. .
... Marc