You can dream over and over that a 120V relay is going to be UL approved to connect a 120V smoke to a FC Panel, but I can tell you it has never and it will never happen. Never. If you think such a relay exists, please post a link for us.
I will say it again the BRK Model RM-4 is UL Listed and the instructions (which are a UL controlled document and its content has to be accepted by UL) have a wiring diagram and everything to connect it to an alarm on page 2 "To install this relay to an alarm connect the power wires as Listed below......" Whenever the interconnect becomes energized by a detector tripping into alarm the relay will activate until the detector resets.
My link
I actually asked a UL Engineer about this weeks ago and he confirmed it and said he believes that there are other mfg with similar relays that are also UL Listed and can be used to trip a FACP and are UL Listed for the application (they can not come out and state mfg name and model numbers as it could be perceived as endorsement). The BRK unit is also Listed to ULC S-531 and S530 for our Canadian neighbors.
Please don't confuse peoples opinions as to what the NFPA 72, IRC and UL really permit. I am not saying you have to like it but please dont state it a fact that something is not permitted. A locality may not permit it and that is up to the AHJ but the national, international and UL requirements dont prohibit it.
I worked in the Security and Signaling categories at UL for many years and I have worked for the last 5 years as a Compliance Engineer for an alarm mfg. We hear lots of misinterpretations of requirements all of the time from well intentioned customers and AHJ's. In the end an AHJ can tell you your detectors have to be purple but once they are pointed to the correct paragraph in the code, IRC or UL Standard they are almost always agreeable to what the code says (a few exceptions I know about in commercial applications).