Actual Cost Savings with controllable thermostats?

inline

Member
Hi Everyone - I'm looking to integrate (2) RCS TR40 thermostats shortly into my ELK system to take advantage of cost savings like lowering the temps when the system is in ARMED-AWAY or ARMED-VACATION mode and other no-brainer situations like that when you might have forgotten to turn the thermostats down. What I'm looking to find out is this: Has anyone noticed or calculated how much they have saved by implementing controllable thermostats into their setup? Has it paid off yet or is it just another fun to have item? As I'll be dropping about $600 or so to implement this, I'd like to know. Thanks!
 
Hard for me to say because I built this house new with the automation as part of the new house. I'm willing to bet the actual savings are fairly minimal however. If your house is well insulated I'm guessing there isn't enough loss that the heater or A/C coming on while you are gone will make a big difference. That probably doesn't hold true for Vacation of course but for the simple no one is home during the day setup probably not a big deal. That will of course change depending on your climate, your insulation, blah blah blah. YMMV...

Chris
 
I have yet to get a controllable thermostat. I do have a programmable one and I can't see any cost savings over that. I just can't see justifying the cost of one of those. Just my 2 cents.
 
Any time you can automatically keep the kids (or wife ) from cranking the cool down or heat up you can save money. I have an event that runs via HomeSeer and depending on the season (cooling/heating) I have HomeSeer set back the stat if it is changed more than 2 degrees. In addition having the ability to adjust your stat from any web access can save you money as schedules do change.
 
I haven't run any programs on my new TR-16 thermostat, but I am definitely seeing a reduction in cost over my old thermostat. The old one was probably 30 yrs old and a simple mercury switch. I found that my system would short cycle constantly when the weather was cold (under 50 degrees). The system would kick on for 5 minutes and cut off for 30-90 seconds before starting again. I live in a 30 yr old house that is not well sealed.

The new TR-16 with the min run time and min rest time has noticably reduced the energy bills around here without a noticable change in actual comfort.

I've always read that the running a program works well with gas heat, but not with a heat pump. That is because if you are not careful with a heat pump, when the system cuts on to heat a house it runs the emergency heat strips which are very inefficient. So any money saved earlier in the day is thrown out the window trying to heat the house back up to normal temps. i guess if you have a smart enough system, then you could slowly increase the temp to make sure the heat strips never actually get turned on.
 
I would agree that purchasing an automatable stat cannot be justified on pure financial basis. If you are already using a stat that sets back on your schedule there is not much to be gained. The ROI is many years...

The same thing can be said for automated lights...if you are good at turning your lights off when not in use it you won't save much money at all.

The real gain I think is in convenience and options. In larger homes it might be a hassle to walk to the the stat to change the temp, if you have multiple zones it might not be easy to program them all and set them correctly, perhaps using alarm armed status to control the setback rather than a fixed schedule works better, what if you want to check the setup remotely. And of course for must of us here there is the cool factor of setting the stat with your blackberry...

Anyway, these reasons are the types of justification for using automated stats.
 
Thanks for the input guys. One of the online places had a special of 20% off that I've been waiting for, so I pulled the trigger on (2) RCS TR40's and the M1XSP. I'm actually the worst when it comes to the thermostats...I totally forget about it, so I know it will help me personally. Also, programming the old thermostats I had wasn't exactly easy and therefore it wasn't ever done, maybe once it was, but then it got erased when batteries in it died or something, who knows. The programming on the TR40 looks easier so there will be more incentive to do it and using setbacks in away mode will help too, especially since the wife or I won't have to run up to the second floor to turn down the thermostat on the second floor (we have two zones, upstairs and downstairs). I'l let everyone know how it goes after I get everything wired up.
 
Don't forget FIRE safety. Activation of the fire alarm will shut down the fans to stop distributing smoke! This feature is most important.
 
Don't forget FIRE safety. Activation of the fire alarm will shut down the fans to stop distributing smoke! This feature is most important.

Yes, once I replace the existing smoke detectors with the GE 350's in about 2 more years when they'll be 10 years old I'll integrate the relay in the 350 into the ELK panel and have it turn off the HVAC as well as kick on all the lights, etc.
 
Thanks for the input guys. One of the online places had a special of 20% off that I've been waiting for, so I pulled the trigger on (2) RCS TR40's and the M1XSP. I'm actually the worst when it comes to the thermostats...I totally forget about it, so I know it will help me personally. Also, programming the old thermostats I had wasn't exactly easy and therefore it wasn't ever done, maybe once it was, but then it got erased when batteries in it died or something, who knows. The programming on the TR40 looks easier so there will be more incentive to do it and using setbacks in away mode will help too, especially since the wife or I won't have to run up to the second floor to turn down the thermostat on the second floor (we have two zones, upstairs and downstairs). I'l let everyone know how it goes after I get everything wired up.
Well, I'm not done yet, but have successfully wired my first thermostat into the ELK. At first I couldn't figure out why I couldn't see it on the M1XEP screen, I had doublechecked wiring as I was going an was 100% sure I did everything right. I didn't fully go thru the ELK documentaton since I didn't want to create rules at this time, however I quickly realized that I had to going into ELK-RP to set a name for the first thermostat... ;) Once I did that, I could see the fruit of my labor and $$$ in the M1XEP screen. As a side note for others, I had ordered (2) of the RCS TR40 units, but was shipped the TR60 units which are labelled weird, parts are labelled TS40 but the unit together is TR60 now, not TR40. I was concernd it might not work, but it seems to work fine, so I guess RCS is just changing the names,etc. Now it's time to clean up he wiring since proof of concept is completed and then wire up the second thermostat. As a side note, the thermostats are nicely made and the WAF so far is high based on the looks of the thermostat and the fact they she could easily manipulate the temperature...LOL.

I'm hoping ELK will increase the support for these thermostat units as it seems a lot of people own these and they work well for retrofit compared to the other solutions.

I'll update this thread as I progress to note any issues, etc I run into, but for now, seems everything is going well.
 
Thanks for the input guys. One of the online places had a special of 20% off that I've been waiting for, so I pulled the trigger on (2) RCS TR40's and the M1XSP. I'm actually the worst when it comes to the thermostats...I totally forget about it, so I know it will help me personally. Also, programming the old thermostats I had wasn't exactly easy and therefore it wasn't ever done, maybe once it was, but then it got erased when batteries in it died or something, who knows. The programming on the TR40 looks easier so there will be more incentive to do it and using setbacks in away mode will help too, especially since the wife or I won't have to run up to the second floor to turn down the thermostat on the second floor (we have two zones, upstairs and downstairs). I'l let everyone know how it goes after I get everything wired up.
Well, I'm not done yet, but have successfully wired my first thermostat into the ELK. At first I couldn't figure out why I couldn't see it on the M1XEP screen, I had doublechecked wiring as I was going an was 100% sure I did everything right. I didn't fully go thru the ELK documentaton since I didn't want to create rules at this time, however I quickly realized that I had to going into ELK-RP to set a name for the first thermostat... :P Once I did that, I could see the fruit of my labor and $$$ in the M1XEP screen. As a side note for others, I had ordered (2) of the RCS TR40 units, but was shipped the TR60 units which are labelled weird, parts are labelled TS40 but the unit together is TR60 now, not TR40. I was concernd it might not work, but it seems to work fine, so I guess RCS is just changing the names,etc. Now it's time to clean up he wiring since proof of concept is completed and then wire up the second thermostat. As a side note, the thermostats are nicely made and the WAF so far is high based on the looks of the thermostat and the fact they she could easily manipulate the temperature...LOL.

I'm hoping ELK will increase the support for these thermostat units as it seems a lot of people own these and they work well for retrofit compared to the other solutions.

I'll update this thread as I progress to note any issues, etc I run into, but for now, seems everything is going well.

Well, I wanted to add a few notes to my progress:

1. Regarding cost savings over a regular programmable thermostat, I agree there won't be much cost savings....if you have a predictable schedule. Unfortunately the schedule here is about as unpredictable as can be. Someone is usually home during the day and myself I'm too forgetful to setback the thermostat before I leave to go somewhere. So I'm hoping to reap the benefits of an automatic setback based on ARMED-AWAY modes, etc. The ROI will probably be very long term based on that solely though. However were I do see the bigger ROI is that the RCS TR40 (now TR60) is so much easier to program a schedule in than our old thermostat. With our old thermostat I felt like I was back in my x86 Assembler class from college...ok not that bad, but it sure wasn't intuitive and you couldn't see the whole schedule, you had to step thru the various times of the day, etc, so basically you had to write down a programming sheet on paper that you could follow as you programmed the thing. Not so with the RCS unit, I read the instructions and could easily program a baseline schedule that will be adjusted based on ARMED-AWAY modes, etc.

2. I wired up the second T60 thermostat and the ELK M1XSP manual shows wiring a +Voltage line for the RS485 data bus, but one simply doesn't exist, so I just used the three conductors between the (2) control units which are about 6" apart. Now here's the thing, the M1XSP manual doesn't show any termination on the RS-485 databus used for the thermostats, but the RCS manual does. I don't have any termination in there right now and it's working, but what I noticed is that after I powered up, one of the thermostats said "Unit not responding". I also got this the first time I powered up when I had just the first thermostat wired. I did a bus enrollment again which didn't help, but what seemd to help was kicking off the thermostat to force it to cool for example. Maybe after a power loss, unless the unit is sending data the M1XSP doesn't poll it? BTW, I did program the thermostat's correctly, the first floor one is set to network address 1 and the second floor is set to network address 2. Regardless, after generating some user input that caused cooling to cycle, the thermostat shows in the M1XEP page (no longer "Unit not repsonding") and everything seems fine now. I know there is a setting where the RCS thermostat can autosend and it's currently set to N, would setting it to Y help in this instance?
 
Thanks for the input guys. One of the online places had a special of 20% off that I've been waiting for, so I pulled the trigger on (2) RCS TR40's and the M1XSP. I'm actually the worst when it comes to the thermostats...I totally forget about it, so I know it will help me personally. Also, programming the old thermostats I had wasn't exactly easy and therefore it wasn't ever done, maybe once it was, but then it got erased when batteries in it died or something, who knows. The programming on the TR40 looks easier so there will be more incentive to do it and using setbacks in away mode will help too, especially since the wife or I won't have to run up to the second floor to turn down the thermostat on the second floor (we have two zones, upstairs and downstairs). I'l let everyone know how it goes after I get everything wired up.
Well, I'm not done yet, but have successfully wired my first thermostat into the ELK. At first I couldn't figure out why I couldn't see it on the M1XEP screen, I had doublechecked wiring as I was going an was 100% sure I did everything right. I didn't fully go thru the ELK documentaton since I didn't want to create rules at this time, however I quickly realized that I had to going into ELK-RP to set a name for the first thermostat... :P Once I did that, I could see the fruit of my labor and $$$ in the M1XEP screen. As a side note for others, I had ordered (2) of the RCS TR40 units, but was shipped the TR60 units which are labelled weird, parts are labelled TS40 but the unit together is TR60 now, not TR40. I was concernd it might not work, but it seems to work fine, so I guess RCS is just changing the names,etc. Now it's time to clean up he wiring since proof of concept is completed and then wire up the second thermostat. As a side note, the thermostats are nicely made and the WAF so far is high based on the looks of the thermostat and the fact they she could easily manipulate the temperature...LOL.

I'm hoping ELK will increase the support for these thermostat units as it seems a lot of people own these and they work well for retrofit compared to the other solutions.

I'll update this thread as I progress to note any issues, etc I run into, but for now, seems everything is going well.

Well, I wanted to add a few notes to my progress:

1. Regarding cost savings over a regular programmable thermostat, I agree there won't be much cost savings....if you have a predictable schedule. Unfortunately the schedule here is about as unpredictable as can be. Someone is usually home during the day and myself I'm too forgetful to setback the thermostat before I leave to go somewhere. So I'm hoping to reap the benefits of an automatic setback based on ARMED-AWAY modes, etc. The ROI will probably be very long term based on that solely though. However were I do see the bigger ROI is that the RCS TR40 (now TR60) is so much easier to program a schedule in than our old thermostat. With our old thermostat I felt like I was back in my x86 Assembler class from college...ok not that bad, but it sure wasn't intuitive and you couldn't see the whole schedule, you had to step thru the various times of the day, etc, so basically you had to write down a programming sheet on paper that you could follow as you programmed the thing. Not so with the RCS unit, I read the instructions and could easily program a baseline schedule that will be adjusted based on ARMED-AWAY modes, etc.

2. I wired up the second T60 thermostat and the ELK M1XSP manual shows wiring a +Voltage line for the RS485 data bus, but one simply doesn't exist, so I just used the three conductors between the (2) control units which are about 6" apart. Now here's the thing, the M1XSP manual doesn't show any termination on the RS-485 databus used for the thermostats, but the RCS manual does. I don't have any termination in there right now and it's working, but what I noticed is that after I powered up, one of the thermostats said "Unit not responding". I also got this the first time I powered up when I had just the first thermostat wired. I did a bus enrollment again which didn't help, but what seemd to help was kicking off the thermostat to force it to cool for example. Maybe after a power loss, unless the unit is sending data the M1XSP doesn't poll it? BTW, I did program the thermostat's correctly, the first floor one is set to network address 1 and the second floor is set to network address 2. Regardless, after generating some user input that caused cooling to cycle, the thermostat shows in the M1XEP page (no longer "Unit not repsonding") and everything seems fine now. I know there is a setting where the RCS thermostat can autosend and it's currently set to N, would setting it to Y help in this instance?
Ok, here's an update to the update:

I called RCS and spoke with Bruce at Tech Support. The autosend should not be set to Y, leave it at N, otherwise network collisions might exist. He said most RS-485 data bus networks are polled, so I guess I need to call ELK and ask how often the M1XSP polls devices on the RS-485 databus. Also, he confirmed that the TR60 is the new and direct replacement for the TR40, functionally it is exactly the same. Also, the termination on the RS-485 databus for the thermostat is not needed unless the run is greater than 100 feet which in my case doesn't apply, so no termination resistor is necessary.

Well, I just got off the phone with ELK and here's the scoup: The XSP polls the 485 databus every 5 seconds for ALL 16 thermostats, so that's 80 seconds. So technically after 80 seconds the thermostat should display (ie not receive "unit not responding"), unless there is traffic on the 485 databus which might delay things further.

I hope all this helps someone in the future!! :throwup:
 
Thanks for the input guys. One of the online places had a special of 20% off that I've been waiting for, so I pulled the trigger on (2) RCS TR40's and the M1XSP. I'm actually the worst when it comes to the thermostats...I totally forget about it, so I know it will help me personally. Also, programming the old thermostats I had wasn't exactly easy and therefore it wasn't ever done, maybe once it was, but then it got erased when batteries in it died or something, who knows. The programming on the TR40 looks easier so there will be more incentive to do it and using setbacks in away mode will help too, especially since the wife or I won't have to run up to the second floor to turn down the thermostat on the second floor (we have two zones, upstairs and downstairs). I'l let everyone know how it goes after I get everything wired up.
Well, I'm not done yet, but have successfully wired my first thermostat into the ELK. At first I couldn't figure out why I couldn't see it on the M1XEP screen, I had doublechecked wiring as I was going an was 100% sure I did everything right. I didn't fully go thru the ELK documentaton since I didn't want to create rules at this time, however I quickly realized that I had to going into ELK-RP to set a name for the first thermostat... :P Once I did that, I could see the fruit of my labor and $$$ in the M1XEP screen. As a side note for others, I had ordered (2) of the RCS TR40 units, but was shipped the TR60 units which are labelled weird, parts are labelled TS40 but the unit together is TR60 now, not TR40. I was concernd it might not work, but it seems to work fine, so I guess RCS is just changing the names,etc. Now it's time to clean up he wiring since proof of concept is completed and then wire up the second thermostat. As a side note, the thermostats are nicely made and the WAF so far is high based on the looks of the thermostat and the fact they she could easily manipulate the temperature...LOL.

I'm hoping ELK will increase the support for these thermostat units as it seems a lot of people own these and they work well for retrofit compared to the other solutions.

I'll update this thread as I progress to note any issues, etc I run into, but for now, seems everything is going well.

Well, I wanted to add a few notes to my progress:

1. Regarding cost savings over a regular programmable thermostat, I agree there won't be much cost savings....if you have a predictable schedule. Unfortunately the schedule here is about as unpredictable as can be. Someone is usually home during the day and myself I'm too forgetful to setback the thermostat before I leave to go somewhere. So I'm hoping to reap the benefits of an automatic setback based on ARMED-AWAY modes, etc. The ROI will probably be very long term based on that solely though. However were I do see the bigger ROI is that the RCS TR40 (now TR60) is so much easier to program a schedule in than our old thermostat. With our old thermostat I felt like I was back in my x86 Assembler class from college...ok not that bad, but it sure wasn't intuitive and you couldn't see the whole schedule, you had to step thru the various times of the day, etc, so basically you had to write down a programming sheet on paper that you could follow as you programmed the thing. Not so with the RCS unit, I read the instructions and could easily program a baseline schedule that will be adjusted based on ARMED-AWAY modes, etc.

2. I wired up the second T60 thermostat and the ELK M1XSP manual shows wiring a +Voltage line for the RS485 data bus, but one simply doesn't exist, so I just used the three conductors between the (2) control units which are about 6" apart. Now here's the thing, the M1XSP manual doesn't show any termination on the RS-485 databus used for the thermostats, but the RCS manual does. I don't have any termination in there right now and it's working, but what I noticed is that after I powered up, one of the thermostats said "Unit not responding". I also got this the first time I powered up when I had just the first thermostat wired. I did a bus enrollment again which didn't help, but what seemd to help was kicking off the thermostat to force it to cool for example. Maybe after a power loss, unless the unit is sending data the M1XSP doesn't poll it? BTW, I did program the thermostat's correctly, the first floor one is set to network address 1 and the second floor is set to network address 2. Regardless, after generating some user input that caused cooling to cycle, the thermostat shows in the M1XEP page (no longer "Unit not repsonding") and everything seems fine now. I know there is a setting where the RCS thermostat can autosend and it's currently set to N, would setting it to Y help in this instance?
Ok, here's an update to the update:

I called RCS and spoke with Bruce at Tech Support. The autosend should not be set to Y, leave it at N, otherwise network collisions might exist. He said most RS-485 data bus networks are polled, so I guess I need to call ELK and ask how often the M1XSP polls devices on the RS-485 databus. Also, he confirmed that the TR60 is the new and direct replacement for the TR40, functionally it is exactly the same. Also, the termination on the RS-485 databus for the thermostat is not needed unless the run is greater than 100 feet which in my case doesn't apply, so no termination resistor is necessary.

Well, I just got off the phone with ELK and here's the scoup: The XSP polls the 485 databus every 5 seconds for ALL 16 thermostats, so that's 80 seconds. So technically after 80 seconds the thermostat should display (ie not receive "unit not responding"), unless there is traffic on the 485 databus which might delay things further.

I hope all this helps someone in the future!! :throwup:

Ok, now I'm am just SO thrilled!!!! This works just how I envisioned and it's just beautiful! Almost as good as the flying cars that I was promised would exist when I was a kid.

I have a baseline schedule programmed into the RCS TR40 (now TR60) thermostats for upstairs and downstairs. I wrote the following rule to setback the thermostats when in ARMED-AWAY mode:


WHENEVER our house (Area 1) IS ARMED AWAY
THEN SET First Floor (Tstat 1) COOLING DESIRED TEMP TO 85 DEG. F. (29 DEG. C.)
THEN SET First Floor (Tstat 1) HEATING DESIRED TEMP TO 65 DEG. F. (18 DEG. C.)
THEN SET First Floor (Tstat 1) HOLD TO ON
THEN SET First Floor (Tstat 2) COOLING DESIRED TEMP TO 85 DEG. F. (29 DEG. C.)
THEN SET First Floor (Tstat 2) HEATING DESIRED TEMP TO 65 DEG. F. (18 DEG. C.)
THEN SET First Floor (Tstat 2) HOLD TO ON

When I put the system into ARMED-AWAY mode, it sets the energy saving setbacks on both themostats and puts them in HOLD mode so the scheduled programmed into the RCS thermostat doesn't override it.

Here's the fule I have to put the thermostats back to the baseline schedule programmed into the RCS thermostats when the system is DISARMED:

WHENEVER our house (Area 1) ARM STATE BECOMES DISARMED
THEN SET First Floor (Tstat 1) HOLD TO OFF
THEN SET Second Floor (Tstat 2) HOLD TO OFF

So when I disarm the system it puts the RCS thermostats back into the scheduled RUN mode using the programmed settings in the thermostats.

Life just doesn't get better than this....I am very pleased! :rockon:

Here is a picture of the (2) RCS Control Units next to the existing Lennox Harmony II Zone Control System:

rcststat1.jpg
 
Inline,

Your insights and follow-through with this are great. I purchased a TR40 many months ago, but I have never had time to actually install it. When I am ready to install, I will definitely be reviewing this thread so that I know what to do.

Thanks!!!

Dave


Thanks for the input guys. One of the online places had a special of 20% off that I've been waiting for, so I pulled the trigger on (2) RCS TR40's and the M1XSP. I'm actually the worst when it comes to the thermostats...I totally forget about it, so I know it will help me personally. Also, programming the old thermostats I had wasn't exactly easy and therefore it wasn't ever done, maybe once it was, but then it got erased when batteries in it died or something, who knows. The programming on the TR40 looks easier so there will be more incentive to do it and using setbacks in away mode will help too, especially since the wife or I won't have to run up to the second floor to turn down the thermostat on the second floor (we have two zones, upstairs and downstairs). I'l let everyone know how it goes after I get everything wired up.
Well, I'm not done yet, but have successfully wired my first thermostat into the ELK. At first I couldn't figure out why I couldn't see it on the M1XEP screen, I had doublechecked wiring as I was going an was 100% sure I did everything right. I didn't fully go thru the ELK documentaton since I didn't want to create rules at this time, however I quickly realized that I had to going into ELK-RP to set a name for the first thermostat... :P Once I did that, I could see the fruit of my labor and $$$ in the M1XEP screen. As a side note for others, I had ordered (2) of the RCS TR40 units, but was shipped the TR60 units which are labelled weird, parts are labelled TS40 but the unit together is TR60 now, not TR40. I was concernd it might not work, but it seems to work fine, so I guess RCS is just changing the names,etc. Now it's time to clean up he wiring since proof of concept is completed and then wire up the second thermostat. As a side note, the thermostats are nicely made and the WAF so far is high based on the looks of the thermostat and the fact they she could easily manipulate the temperature...LOL.

I'm hoping ELK will increase the support for these thermostat units as it seems a lot of people own these and they work well for retrofit compared to the other solutions.

I'll update this thread as I progress to note any issues, etc I run into, but for now, seems everything is going well.

Well, I wanted to add a few notes to my progress:

1. Regarding cost savings over a regular programmable thermostat, I agree there won't be much cost savings....if you have a predictable schedule. Unfortunately the schedule here is about as unpredictable as can be. Someone is usually home during the day and myself I'm too forgetful to setback the thermostat before I leave to go somewhere. So I'm hoping to reap the benefits of an automatic setback based on ARMED-AWAY modes, etc. The ROI will probably be very long term based on that solely though. However were I do see the bigger ROI is that the RCS TR40 (now TR60) is so much easier to program a schedule in than our old thermostat. With our old thermostat I felt like I was back in my x86 Assembler class from college...ok not that bad, but it sure wasn't intuitive and you couldn't see the whole schedule, you had to step thru the various times of the day, etc, so basically you had to write down a programming sheet on paper that you could follow as you programmed the thing. Not so with the RCS unit, I read the instructions and could easily program a baseline schedule that will be adjusted based on ARMED-AWAY modes, etc.

2. I wired up the second T60 thermostat and the ELK M1XSP manual shows wiring a +Voltage line for the RS485 data bus, but one simply doesn't exist, so I just used the three conductors between the (2) control units which are about 6" apart. Now here's the thing, the M1XSP manual doesn't show any termination on the RS-485 databus used for the thermostats, but the RCS manual does. I don't have any termination in there right now and it's working, but what I noticed is that after I powered up, one of the thermostats said "Unit not responding". I also got this the first time I powered up when I had just the first thermostat wired. I did a bus enrollment again which didn't help, but what seemd to help was kicking off the thermostat to force it to cool for example. Maybe after a power loss, unless the unit is sending data the M1XSP doesn't poll it? BTW, I did program the thermostat's correctly, the first floor one is set to network address 1 and the second floor is set to network address 2. Regardless, after generating some user input that caused cooling to cycle, the thermostat shows in the M1XEP page (no longer "Unit not repsonding") and everything seems fine now. I know there is a setting where the RCS thermostat can autosend and it's currently set to N, would setting it to Y help in this instance?
Ok, here's an update to the update:

I called RCS and spoke with Bruce at Tech Support. The autosend should not be set to Y, leave it at N, otherwise network collisions might exist. He said most RS-485 data bus networks are polled, so I guess I need to call ELK and ask how often the M1XSP polls devices on the RS-485 databus. Also, he confirmed that the TR60 is the new and direct replacement for the TR40, functionally it is exactly the same. Also, the termination on the RS-485 databus for the thermostat is not needed unless the run is greater than 100 feet which in my case doesn't apply, so no termination resistor is necessary.

Well, I just got off the phone with ELK and here's the scoup: The XSP polls the 485 databus every 5 seconds for ALL 16 thermostats, so that's 80 seconds. So technically after 80 seconds the thermostat should display (ie not receive "unit not responding"), unless there is traffic on the 485 databus which might delay things further.

I hope all this helps someone in the future!! :throwup:

Ok, now I'm am just SO thrilled!!!! This works just how I envisioned and it's just beautiful! Almost as good as the flying cars that I was promised would exist when I was a kid.

I have a baseline schedule programmed into the RCS TR40 (now TR60) thermostats for upstairs and downstairs. I wrote the following rule to setback the thermostats when in ARMED-AWAY mode:


WHENEVER our house (Area 1) IS ARMED AWAY
THEN SET First Floor (Tstat 1) COOLING DESIRED TEMP TO 85 DEG. F. (29 DEG. C.)
THEN SET First Floor (Tstat 1) HEATING DESIRED TEMP TO 65 DEG. F. (18 DEG. C.)
THEN SET First Floor (Tstat 1) HOLD TO ON
THEN SET First Floor (Tstat 2) COOLING DESIRED TEMP TO 85 DEG. F. (29 DEG. C.)
THEN SET First Floor (Tstat 2) HEATING DESIRED TEMP TO 65 DEG. F. (18 DEG. C.)
THEN SET First Floor (Tstat 2) HOLD TO ON

When I put the system into ARMED-AWAY mode, it sets the energy saving setbacks on both themostats and puts them in HOLD mode so the scheduled programmed into the RCS thermostat doesn't override it.

Here's the fule I have to put the thermostats back to the baseline schedule programmed into the RCS thermostats when the system is DISARMED:

WHENEVER our house (Area 1) ARM STATE BECOMES DISARMED
THEN SET First Floor (Tstat 1) HOLD TO OFF
THEN SET Second Floor (Tstat 2) HOLD TO OFF

So when I disarm the system it puts the RCS thermostats back into the scheduled RUN mode using the programmed settings in the thermostats.

Life just doesn't get better than this....I am very pleased! :rockon:

Here is a picture of the (2) RCS Control Units next to the existing Lennox Harmony II Zone Control System:

View attachment 2468
 
Thanks Inline,
This has motivated me to get my tstat installed sometime soon, I have an LP furnace and with as cold as it was last winter I was consuming around $140 worth of propane a week. So even minimal increases in efficiency would be beneficial. I'll try to collect some rough data on consumption this winter.
 