apostolakisl
Senior Member
How is electric service provided at the gate? I'm thinking if your friend has to cut a trench from the house to the gate to get power there, then the same trench might be suitable for low voltage or fiber. On the other hand, if gate power comes from a pole across the street, then a trench just for the low voltage might make the wireless solution more practical.
I agree with the above.
Also, there would be a great expense in running electric wire 2000 ft trench not even considered. For example, 2000 ft, 10 amps, 120v, 3% voltage drop requires between 0 and 00 gauge. 2000 ft of 0 gauge is $$$$. Maybe you don't mind a bigger voltage drop or figure you won't use hardly any amps out there. You could run 10 awg wire if you were planning on staying under 1 amp with 3% v drop. But one amp is only 120watts (minus your 3%).