Concerning the neutral wiring to your boxes. Make sure that they do not share a neutral wire run from ANY 220 volt box/outlet.
For instance in my new house they shared a neutral run for my 120 VAC to my refrigerator from a nearby 220 VAC outlet for my gas ovens. The problem is that when I went to replace the refrigerator's electrical outlet (to an X-10 type) I made sure the breaker was off and verified by pluging a lamp into that outlet to make sure the light was off before removing it.
When I took the outlet off I removed all the wires and when I touched the White neutral wire I got shocked! Found out that it was "backfeeding" from the nearby 220 Volt box and the moment I removed its ground reference (by taking the wire off of the outlet) I created a 120 Volt potential between that wire and ground.
I have never heard of running wiring this way, but I guess its done to save the amount of neutral feeds needed from the kitchen to the breaker box.
One strong piece of advice I would give anyone is that when you are installing X-10 outlet and switches that require you to remove existing units is this: If you are removing any item which already has a neutral feed attached to it (i.e. an outlet) especially in the kitchen area, make sure that when you disconnect the neutral wire that you do not have any voltage between that wire and ground! I would even go one step further and shut off the breakers to any nearby 220 volt sources, just in case that neutral is being shared from that box.
Since I am on this subject:
Another situation I ran into was when I wanted to place X-10 light switches in a four switch gang box. For convienence I wanted to remove all four switches at once. Three of the switches went to overhead lighting and one switch went to a wall outlet (that didn't have anything pluged into it). I turned all the switches on and tripped the breaker that turned off all three of the overhead lights. I then ASSUMED that no power was in the box.
Well, when I touched the black (source) wire that went to the last switch that powered the outlet I got shocked. Found out that its source WAS ON ANOTHER BREAKER (its feed was not the same source/breaker as the other three switches). I had to shut off another breaker to make that entire box colded. (I also assumed that it was against code to have two separate sources installed in one junction box).
Bottom line is to be carefull and if you can, physically check for voltages with a meter first (usually to each wire and "ground").
Regards,
BSR
For instance in my new house they shared a neutral run for my 120 VAC to my refrigerator from a nearby 220 VAC outlet for my gas ovens. The problem is that when I went to replace the refrigerator's electrical outlet (to an X-10 type) I made sure the breaker was off and verified by pluging a lamp into that outlet to make sure the light was off before removing it.
When I took the outlet off I removed all the wires and when I touched the White neutral wire I got shocked! Found out that it was "backfeeding" from the nearby 220 Volt box and the moment I removed its ground reference (by taking the wire off of the outlet) I created a 120 Volt potential between that wire and ground.
I have never heard of running wiring this way, but I guess its done to save the amount of neutral feeds needed from the kitchen to the breaker box.
One strong piece of advice I would give anyone is that when you are installing X-10 outlet and switches that require you to remove existing units is this: If you are removing any item which already has a neutral feed attached to it (i.e. an outlet) especially in the kitchen area, make sure that when you disconnect the neutral wire that you do not have any voltage between that wire and ground! I would even go one step further and shut off the breakers to any nearby 220 volt sources, just in case that neutral is being shared from that box.
Since I am on this subject:
Another situation I ran into was when I wanted to place X-10 light switches in a four switch gang box. For convienence I wanted to remove all four switches at once. Three of the switches went to overhead lighting and one switch went to a wall outlet (that didn't have anything pluged into it). I turned all the switches on and tripped the breaker that turned off all three of the overhead lights. I then ASSUMED that no power was in the box.
Well, when I touched the black (source) wire that went to the last switch that powered the outlet I got shocked. Found out that its source WAS ON ANOTHER BREAKER (its feed was not the same source/breaker as the other three switches). I had to shut off another breaker to make that entire box colded. (I also assumed that it was against code to have two separate sources installed in one junction box).
Bottom line is to be carefull and if you can, physically check for voltages with a meter first (usually to each wire and "ground").
Regards,
BSR