I'm still struggling with this OmniLT. PaulD and ano were a big help in solving the phone issue. Now I am having problems with the smoke alarms. I have installed two "System Sensor", two wire sensors. They are wired green to 1st sensor in, green 1st sensor out to 2nd sensor in, white to 1st common to second common, with a 1000 ohm resistor across the leads at the last sensor. That is the way it is shown in the literature. At the omni panel, green is connected to zone 8 and white to Out 2. The jumper is set to smoke. I get the message "Zone 8 Fire/smoke not ready," on the controller. I have gone to control and configured Output 2 as Switched Power Output, Zone 8 is set as "Fire." The manual calls for "Supervised Fire," but that is not a choice. I have armed the system and disarmed it to reset the fire but cannot get rid of the message. The LED's on the sensors do not blink or light up. There is no voltage across Z8 and output 2. I am sure this is some configuration problem, but I sure can't figure it out. I just discovered the HAI forum over on Marketplace. Sorry if I got this in the wrong place. Am posting a different problem over there