I've got an Omnistat RC1000 and am trying to use it to control my Hot Water boiler that runs my heating. The boiler didn't come with a 24v control line - It only had two high voltage thermostat terminals for a 120v/240v thermostat.
I hooked up a 24v relay and I also hooked up a dedicated 24v transformer that does nothing other than supply 24v AC to the relay & thermostat. There is plenty of power - since the transformer is dedicated to just that.
I hooked up a simple 2 wire Honeywell thermostat (old school with mercury and no electronics) and tested the circuit. It all works fine with the simple 2 wire Honeywell thermostat.
Unfortunately, when I plug in the Omnistat and connect my 2 wires to W1 and RH - the light comes on, then turns off and it endlessly cycles this way. It sounds like the common problem I've ready about - lack of having a 24VAC common wire.
When I run outside to the boiler and look at the relay/transformer box I hooked up - I can hear the relay clicking and cycling away in sync with the omnistat flashing on and off. At a guess - it seems that the power stealing circuitry is triggering the relay, and I don't have other circuits it can steal power from.
I also don't have a spare wire to hook up a common - just the two wires for W1 and RH from boiler to furnace.
I looked at the specs on the optional HAI power supply module - but it appears to have too many wires for my application - and won't fit in the boiler. Looking at the product description, it sounds like what I might need is a current limiting resistor that goes in series with the 24v relay terminals.
If the fix is that easy - what value resistor should be used? or am I going about this the wrong way...
I hooked up a 24v relay and I also hooked up a dedicated 24v transformer that does nothing other than supply 24v AC to the relay & thermostat. There is plenty of power - since the transformer is dedicated to just that.
I hooked up a simple 2 wire Honeywell thermostat (old school with mercury and no electronics) and tested the circuit. It all works fine with the simple 2 wire Honeywell thermostat.
Unfortunately, when I plug in the Omnistat and connect my 2 wires to W1 and RH - the light comes on, then turns off and it endlessly cycles this way. It sounds like the common problem I've ready about - lack of having a 24VAC common wire.
When I run outside to the boiler and look at the relay/transformer box I hooked up - I can hear the relay clicking and cycling away in sync with the omnistat flashing on and off. At a guess - it seems that the power stealing circuitry is triggering the relay, and I don't have other circuits it can steal power from.
I also don't have a spare wire to hook up a common - just the two wires for W1 and RH from boiler to furnace.
I looked at the specs on the optional HAI power supply module - but it appears to have too many wires for my application - and won't fit in the boiler. Looking at the product description, it sounds like what I might need is a current limiting resistor that goes in series with the 24v relay terminals.
If the fix is that easy - what value resistor should be used? or am I going about this the wrong way...