Hello I was wondering if someone could look over these rules and let me know if they should work properly. I do not have access to the system at the moment but I wanted to have these rules and definitions setup properly before I test.
I have confirmed the temperatures are reading properly and the relay for output 18 is working.
What I would like it to do is check if the temperature outside is above 67 and if it is then don’t run the pumps at all
Zone 003 – Room to be heated (2A)- ELK-M1ZTS
Def: 33 = Temperature
Type: 2 – Normally Open
Zone 013 HEATSWITCH
Definition: 16 = Non Alarm
Type: 2 – Normally Open
Zone 016 – Outdoor Air Temp - ELK-M1ZTS
Definition: 16 = Non Alarm
Type: 2 – Normally Open
Output 18 - Circulation pump for heat
5) WHENEVER HEATSWITCH (Zn 13) BECOMES SECURE
AND 2A Space Temp (Zn 3) ACTUAL TEMPERATURE IS LESS THAN 76 DEG. F
THEN TURN 2A Circ Pump (Out 18) ON
6) WHENEVER HEATSWITCH (Zn 13) BECOMES SECURE
AND 2A Space Temp (Zn 3) ACTUAL TEMPERATURE IS GREATER THAN 76 DEG. F
THEN TURN 2A Circ Pump (Out 18) OFF
15) WHENEVER EVERY 45 SECONDS
THEN UNBYPASS HEATSWITCH (Zn 13)
16) WHENEVER EVERY 60 SECONDS
AND Outdoor Air Temp (Zn 16) ACTUAL TEMPERATURE IS GREATER THAN 67 DEG F
THEN BYPASS HEATSWITCH (Zn 13)
I would be adding more rules for zones similar to zone Zn 3 and separate outputs but want to make sure the set of rules would work first.
Thanks.
I have confirmed the temperatures are reading properly and the relay for output 18 is working.
What I would like it to do is check if the temperature outside is above 67 and if it is then don’t run the pumps at all
Zone 003 – Room to be heated (2A)- ELK-M1ZTS
Def: 33 = Temperature
Type: 2 – Normally Open
Zone 013 HEATSWITCH
Definition: 16 = Non Alarm
Type: 2 – Normally Open
Zone 016 – Outdoor Air Temp - ELK-M1ZTS
Definition: 16 = Non Alarm
Type: 2 – Normally Open
Output 18 - Circulation pump for heat
5) WHENEVER HEATSWITCH (Zn 13) BECOMES SECURE
AND 2A Space Temp (Zn 3) ACTUAL TEMPERATURE IS LESS THAN 76 DEG. F
THEN TURN 2A Circ Pump (Out 18) ON
6) WHENEVER HEATSWITCH (Zn 13) BECOMES SECURE
AND 2A Space Temp (Zn 3) ACTUAL TEMPERATURE IS GREATER THAN 76 DEG. F
THEN TURN 2A Circ Pump (Out 18) OFF
15) WHENEVER EVERY 45 SECONDS
THEN UNBYPASS HEATSWITCH (Zn 13)
16) WHENEVER EVERY 60 SECONDS
AND Outdoor Air Temp (Zn 16) ACTUAL TEMPERATURE IS GREATER THAN 67 DEG F
THEN BYPASS HEATSWITCH (Zn 13)
I would be adding more rules for zones similar to zone Zn 3 and separate outputs but want to make sure the set of rules would work first.
Thanks.