DIYHP,
Again I apologize. I was trying to clear confusion and apparently crated more.
Confusion point 1: The following schematic from SA does
NOT propose that you tie the neutrals from two different circuits together. The connection to the right hand side of the schematic are "Optional" (shown dotted). The section dealing with this also clearly specifies that the HOT must be from the same breaker.
Quite from the installation guide:
OPTIONAL: In some multi-way circuits there may not be an 'always hot’ wire available in both junction boxes, requiring use of one of the wires in the traveler Romex to provide a hot
connection to the other junction box, or possibly the hot wire of an adjacent switch in the same junction box as the remote USR. All hot power wires used MUST be powered from the
same circuit breaker
LARGE CAUTION against using hot feeds from different circuits.
If a neutral wire is available in the remote USR junction box (e.g. neutral wire from a power feed to an adjacent switch), other than the white wire in the traveler Romex or the white neutral wire going up to the load/lights, then the white neutral wire in the traveler Romex maybe re-labeled (as black, typically with black electrical tap on white wire insulation at both ends) and used to carry power (hot) from the master switch junction box over to the USR to enable the blue LED function.
Confusion point #2: Remote switch supplied wit 120V by branch A while using a neutral from a separate branch.
This one is a bit stickier and the reason for all of the discussion.
1) Both the SA schematic and DIYHP's schematic clearly show the US40 remote being supplied by 120V from Branch A with a neutral from "somewhere".
2) The SA instructions do not place any restrictions on the source of this neutral.
3) DIYHP has done the work to make sure that this neutral is associated with a branch on the same phase (i.e. if the neutral is lifted the switch cannot see 240V - phases in series).
This is a bit of a gray area. If you examine the "Intent" of the NEC code:
1) The neutral must be sized to properly handle load currents.
2) Multi Wire Branch circuits (MWB) using a single neutral and opposite phase 120V legs are allowed due to the current cancellation that occurs in the neutral. A number of additional requirements apply and (as of 2008) a double pole breaker must be used.
The bottom line intent of the code - ensure that the neutral is properly sized - it's not protected by a breaker.
For those interested, Stubbie has a nice descriptive post (with graphics) over at diychatroom:
Stubbie: Sharing Neutrals
Stubbie did a masterful job of illustrating why branch circuits on the same phase should not share a common. The illustration is a violation of rule 1) above (excessive current on the common). I have not been able to find a code section that specifically disallows a shared neutral connection
as long as the neutral is properly sized.
As SA (and others) have stated, the US40 remote is not a LOAD device. It presumably contributes an insignificant current to the neutral. As a result, rule 1) should not be violated.
I, and many others, have been trained that shared neutrals (except for the MWB configuration) are an extremely bad thing. For loaded devices they are. This has been pounded into us to the extent that we've accepted it as "Code" - I can't find evidence of that, but then I'm about 35 years out of date. At the moment, I can't see where this specifically violates NEC code.
The real problem here may be yours inspector. Chances are he will have a similar mindset and, if he catches it, will reject the configuration out of hand. You can choose to explain the configuration (this may be hard) or switch the re-tasked wire back to a neutral connection (eliminate the other neutral at the remote) and give up the LED. Your choice.
IM