I'm unable to add the CQC ELK Driver; Driver State: Waiting for Comm Resource. Not problem communicating with the ELK-M1 via ELK-RP. The Port, Protocol and Address is the same as in the M1XEP Setup.
You can leave the driver in place while you use RP. RP will ask the driver to back off until further notice, and then when RP exits it'll let the driver go again. But the driver cannot initially connect if you bring it up while RP is active, since it doesn't know why it's not getting any love, and assumes the Elk isn't there.
Its it possible for say the HSeer elk plugin and the cqc driver to send and receive infomation from the elk at the same
time, through the eth interface?...or through different ports?....or if hs was using the eth interface and cqc was using the
serial interface.
Also I think their may be some type of program that manages the ports that allows mulitple conections at the same time, would something like this work?
When the M1 is in Installer Program Mode (via keypad or ELK RP) it ignores incoming commands on its Ethernet ports (factory defaults: non-secure: 2101; secure: 2601).
During this mode, external software cannot control or monitor the M1. Any commands issued to the M1 result in an "RP" command reply (RP0100) which indicates the M1 is busy.
When the M1 exits Installer Program Mode, it broadcasts an "IE" command (IE00) indicating its readiness to receive commands.