You need to be clear on if you are discussing smoke alarms or smoke detectors. The two are very distinct and different items and vastly different QC and requirements. To be clear, I install, service, maintain and test extremely large systems and sites for fire alarm.
The 10 year milestone is ONLY for detectors that can't be tested for sensitivity in the field. The reason why the 10 year mark is used is because if you can't read the sensitivity of the chamber or the drift compensation your device may be out of the manufacturer's spec and may or may not alarm. If the detector is within spec and can have the values pulled then the detector may remain in service.
Depending on the detector and technology involved, the test switch can simulate an actual chamber alarm, not just activate the circuit.....it depends on the panel and intelligence in the field. Many older units had obscuration cards that were installed for testing purposes before test switches came in vogue. The same holds true for CO detectors.
I would have to see the documentation and what is specified in the latest adopted NFPA 72, but technically Elk's 2 way smokes do not supercede the building code requirements for hardwired fire alarm and design elements. I'd have to see what the actual verbiage is, however if the detectors do not annunciate a trouble condition on a fail to communicate to the host panel (which is what dictates the logic here) that is going to be the nail in the coffin. There is no fail-safe to allow the detectors to tandem ring in any of the documentation that I have seen come to market so far.
FWIW, one of our sites has upwards of 20K installed detectors and failure is less than a tenth of a percent in a commercial building occupied 24/7 with all different enviromental criteria. Most of the times it's a detector falling out of spec that necessitates it's replacement (easier than cleaning in mission critical applications vs. price of detector).
The 10 year milestone is ONLY for detectors that can't be tested for sensitivity in the field. The reason why the 10 year mark is used is because if you can't read the sensitivity of the chamber or the drift compensation your device may be out of the manufacturer's spec and may or may not alarm. If the detector is within spec and can have the values pulled then the detector may remain in service.
Depending on the detector and technology involved, the test switch can simulate an actual chamber alarm, not just activate the circuit.....it depends on the panel and intelligence in the field. Many older units had obscuration cards that were installed for testing purposes before test switches came in vogue. The same holds true for CO detectors.
I would have to see the documentation and what is specified in the latest adopted NFPA 72, but technically Elk's 2 way smokes do not supercede the building code requirements for hardwired fire alarm and design elements. I'd have to see what the actual verbiage is, however if the detectors do not annunciate a trouble condition on a fail to communicate to the host panel (which is what dictates the logic here) that is going to be the nail in the coffin. There is no fail-safe to allow the detectors to tandem ring in any of the documentation that I have seen come to market so far.
FWIW, one of our sites has upwards of 20K installed detectors and failure is less than a tenth of a percent in a commercial building occupied 24/7 with all different enviromental criteria. Most of the times it's a detector falling out of spec that necessitates it's replacement (easier than cleaning in mission critical applications vs. price of detector).