mikefamig said:I used Ditek device to protect the Elk security system
http://www.ditekcorp.com/Docs/ProdGuides/LVLP%20Series%20Datasheet.pdf
What service voltage did you go with 5V or 12V?
mikefamig said:I used Ditek device to protect the Elk security system
http://www.ditekcorp.com/Docs/ProdGuides/LVLP%20Series%20Datasheet.pdf
rsw686 said:What service voltage did you go with 5V or 12V?
rsw686 said:I've read over the NEC code and it clearly states that both builds must have a ground rod driven. I found an IAEI post, which has pictures showing my current setup per NEC 2005 code. The catch is there can be no other metallic paths between the buildings. I could run fiber for network, but that leaves me stuck on the security side. I could forgo the OmniPro expansion enclosure and just home run a few zones, but I feel like I am fighting the inevitable.
It looks like the best/correct answer, which is what NEC 2008 requires, is to just run a new feeder with 4 conductors. I'm going to follow NEC code and leave the ground rod connected at the shop. I also will need to rewire the shop panel so the neutral and grounds are separated.
After looking at the below picture it makes sense that with 3 conductors between the buildings ethernet, security cable, etc would become a potential source for stray current to destroy the equipment. It just doesn't seem worth the risk to fry equipment over a few hundred dollars of cable. Since I do have a disconnect at the house for the shop feeder I can abandon the 4/0 3 conductor cable, install a new 125A breaker, run 1/0 aluminum 4 conductor cable, and hookup the shop panel myself. After that is working I can pay an electrician to pull the meter, remove the splice box and fused disconnect, and connect the house panel directly to the meter.
If your devices are leaking current to earth grounds through their cabinets then I would consider that as a fault in the system that should be corrected. How else can you be sure that there will never be current on a ground if you allow your devices to conduct it there?Lou Apo said:This hookup is fine until you run other wires between the two buildings. The two grounds are bonded, but that doesn't mean electricity will only follow that path between the two of them. Even though you haven't tied to the neutral to the ground, electricity can still arc the microscopic spaces between neutral and ground in your equipment and use your LV stuff as a parallel path to the ground wire. You can use the surge protectors mentioned and cross your fingers, or you can go fiber.
mikefamig said:If your devices are leaking current to earth grounds through their cabinets then I would consider that as a fault in the system that should be corrected. How else can you be sure that there will never be current on a ground if you allow your devices to conduct it there?
Also current will take all paths to earth but most of the current will take the path of least resistance to earth. If you have properly driven ground stakes into the earth at each building and connect all equipment grounds to them then any current that leaks into the system in each building will go safely into the earth through those stakes before traveling to the other building.
Mike.
mikefamig said:If your devices are leaking current to earth grounds through their cabinets then I would consider that as a fault in the system that should be corrected. How else can you be sure that there will never be current on a ground if you allow your devices to conduct it there?
Also current will take all paths to earth but most of the current will take the path of least resistance to earth. If you have properly driven ground stakes into the earth at each building and connect all equipment grounds to them then any current that leaks into the system in each building will go safely into the earth through those stakes before traveling to the other building.
Mike.
pete_c said:or is the fiber media converter powered over ethernet?
No. It is just powered at each end. You could probably power each end via POE.
fiberconverters.jpg
Lou Apo said:The trouble is you'll never find your "leak" to ground. Lightening strikes generate large voltage potentials and at some point a non-conductor becomes a conductor. It could be an arc through air or some other medium that does not conduct on your testing. When presented with 1000 volts or 10,000 volts, or who knows, suddenly it changes its properties and conducts.
Lou ApoLou Apo said:The trouble is you'll never find your "leak" to ground. Lightening strikes generate large voltage potentials and at some point a non-conductor becomes a conductor. It could be an arc through air or some other medium that does not conduct on your testing. When presented with 1000 volts or 10,000 volts, or who knows, suddenly it changes its properties and conducts.