2nd of August, 2014 - 1300c
The endeavor begins. Note first pictures. I took the cover off of the outside breaker. I see two black ~ 8 -10 gauge wires connected to the 220 VAC disconnect.
Odd thing is that there is a neutral inside of the box and no neutral wires present and not coming in from the fuse panel conduit. I think this is the original wiring.
Questions right now. Looked around for some 8-10 gauge white stranded electrical cable and all I have is 12 gauge. The run from the box to the fuse panel is about 2 feet or so. The PITA part is that I have to remove the cover of the fuse panel and outside compressor to run a neutral wire. The surge protector has three wires; two hot and one neutral. There is no neutral wire (white) going to the compressor. Speaking to a peer about this endeavor (he did the same). He had 2 hot, 1 neutral and 1 ground going to the outside box.
Took the cover off of the AC unit to look at the wiring and there is a neutral bus bar there with nothing connected to it. It should be easy then to run a neutral wire from there to the outside fuse box.
Will also post a picture of the blown capacitor (which was replaced a couple of weeks ago). The base is so rounded that it doesn't sit flat on any surface. The top is also bulging a bit.
1 - Will it be OK to run the 12 gauge white neutral wire to the fuse panel ?
or
2 - should I purchase some 8 gauge wire?
and
3 - Seeing this; is this a "faux pas" thing?
Here is a picture of what I see. The new outside unit is higher than the old one such that I cannot remove the door; just flip it up to work in the box (real PITA). Well and the conduit through the brick is there so it would be sort of a real pain to move the move. I did look at moving it when the new unit was installed.
Fuse panel neutral block and grounding picture.
- Purchased 15 feet (way too much) of 8 gauge stranded white wire and some terminal ends. ($11.00 USD)
- removed fuse panel cover
3nd of August, 2014 0700c (AC off for 30 minutes)
Picture of exterior disconnect and AC contactor / capacitor and ground block.
- shut off AC via thermostat, switch at furnace, air cleaner and tandem 40 amp breaker
- ran neutral 8 gauge white wire from neutral block in exterior AC disconnect box to neutral block in AC unit
Here I had to disconnect the 2 black hot 8 guage wires and remove the conduit to pass the neutral 8 gauge wire through.
This part was a bit more time consuming but made it much easier to run the new neutral cable.
- installed surge protector removing knockout on exterior disconnect box
- connect two black wires to hot leads on the egress of the fuse.
- connect Sepco ground white wire to neutral block
- turned on tandem 40 fuse panel breaker, switch at furnace and air cleaner.
- turned AC on at thermostat
- validated function of LED lamp on surge protector (working)
- put the fuse panel cover back on
What I didn't do -
- I didn't run a white neutral 8 guage wire from the neutral block in the exterior disconnect to the fuse panel neutral block.