Morning of the day after.
A bit time consuming and note you have to be comfortable doing this and if not hire an electrician. Saftey first - make sure you have your main breakers off (top of the panel) when working in the panel.
I needed to pass the 4 tails from the TVSS to the fuse panel this morning. It was a bit difficult to do with the 3/4" pipe and two short 90's. I ran two at a time using a 16/2 speaker cable as my fishing wire. I stagged taped two tails and pulled in the panel while pushing from the TVSS box. Its kind of slow going. The next two I did in a similiar fashion only slower.
This part would be much faster with a single straight and short 3/4" interconnection between TVSS (PTX-160) and fuse panel. Noticed that all of the cables are labeled (Black A and B, neutral white and earthground green).
Next steps are to shorten the neutral lead and ground leads. Both of these will going to the grounding / neutral block shown with the white wires in it. While I am in the vicinity will make the wires a bit tighter such that the copper doesn't show. The run from the opening to the neutral block is about 2-3" plus the run inside of the TVSS thru to the fuse panel (about 6" or so).
One "faux pas" was the two 90's. I did not have a choice though.
Connected my neutral and ground keeping the leads as short as possible (will post pics). Difficult because I had to physically place the wires on the grounding bars and then push in a bit with needle nose pliers behind the break loads. Not much room to play with.
The following guidelines should be followed when installing conduit between the SPD and electrical panel:
• Avoid using 90° elbows and keep the conduit run as short and straight as possible.
See Figure 2-1.
• If the electrical system utilizes an isolated ground, then the SPD’s housing must be
isolated from ground using insulated conduit fittings.
• When applicable, use weatherproof (corrosion resistant) conduit and fittings to maintain the
enclosure’s NEMA 4 or 4X rating.
• If the SPD enclosure does not already have a hole for installing conduit, punch or drill a hole of
the appropriate size to accommodate the size of conduit being installed.
Split Phase (1S101)
Important! Do not install SPD if the Neutral to
Ground (Earth) bond is not present as the
SPD may be damaged.
a. Connect the SPD’s Ground (GRN) wire
directly to the electrical panel’s Ground
bus bar.
b. Connect the SPD’s Neutral (WHT) wire
directly to the electrical panel’s Neutral bus
bar.
c. Connect the SPD’s Phase A (BLK) wire
through an overcurrent protective deviceto the electrical
panel’s Phase A voltage bus bar.
d. Repeat Step c to connect the SPD’s
Phase B (BLK) wire to its associated bus bar.