DELInstallations said:
The fire trouble is indicating you don't have a continous circuit, no matter what the walk test button indicates. You need to fix that first.
DEL - All Smokes & CO are blinking at the normal rate. Not sure what do you mean by continuous circuit? Trying to wrap my head around the smoke / CO and how the cosmod2 works.
Sorry about the confusion. All I was trying to say is that I could not snap the base and smoke, testing it out. Just trying to see if they snapped on. It’s all set now. I mounted the base they do snap on. Needed little love.
As far as the cosmo2w I am confused. I marked every Red wire that was the first (power source) and not the loop. I installed the cosmo2w and made sure I marked wires that went to the local positive terminal and not the loop. So the next 2wtab or cosmo2w would be connected same as the 3.9k resistor as per fig 3. See attached. Also the last COSMO2W has an EOL 3.9k. I have four Cosmo2w and three 2WTAB in loop.
Does the Loop Style D wires get connected?
Also there are couple dip switches on the cosmod that I am not sure of the settings.
Here is how it is configured
Cosmod2 Connections
Power – SAUX
Smoke – Zone 16
Maint - Havent figured out. Not sure how to define the zone.
CO Alarm – Zone 15
CO Trigger – Not sure how to configure
Smoke EOL – 2.2k
CO EOL – 2.2k
IDC +/- = Smoke & CO Detectors
Style +/- = No Connection
Smoke Trigger – Out 3 N/O