You probably want the 5601p as:
*No lettering
*Resettable RoR and hence easily testable
http://www.systemsensor.com/pdf/I56-2175.pdf
Page 3 Bottom Right Corner
Sadly the RRS-MOD probably is something you need.
http://www.systemsensor.com/pdf/A05-0350.pdf
jlehnert is right any smoke trips and you should hear the tones throughout the house, I'm thinking the installer expected to use the sounder inside the smoke to cover this. I don't think it's going to work that way for him.
Now it is very well possible that they used 22-4 wire and put all the smokes on red/black and the thermals on green/white, this would be 2 zones inside 1 wire and should work with the RRS-MOD on the red/black.
Otherwise just get cheaper smokes and add more sirens, less current draw which should kill both concerns in one swoop.
*No lettering
*Resettable RoR and hence easily testable
http://www.systemsensor.com/pdf/I56-2175.pdf
Page 3 Bottom Right Corner
Caution!
When using the RRS-MOD with model 2WTA-B, do
not mix the 2WTA-B with other model smoke detectors
and dry contact closure devices, including
mechanical heat detectors, manual pull stations and
waterflow switches. Such mixing can cause a direct
short on the auxiliary power terminals, damaging
the control panel’s internal circuitry and/or damage
devices connected to the initiating device circuit.
Sadly the RRS-MOD probably is something you need.
http://www.systemsensor.com/pdf/A05-0350.pdf
jlehnert is right any smoke trips and you should hear the tones throughout the house, I'm thinking the installer expected to use the sounder inside the smoke to cover this. I don't think it's going to work that way for him.
Now it is very well possible that they used 22-4 wire and put all the smokes on red/black and the thermals on green/white, this would be 2 zones inside 1 wire and should work with the RRS-MOD on the red/black.
Otherwise just get cheaper smokes and add more sirens, less current draw which should kill both concerns in one swoop.