Haiku Changing thermostat temp

rsw686

Active Member
I've noticed when changing the temp multiple degrees Haiku will not always reflect the desired temp. For example if it is set at 66 and I hit up to 68 it might go to 67. What I think happens is it sends the first temp change immediately and the OmniPro sends a status update before the second temp change is sent reverting my change. Would it be possible to add a delay of a second before sending the command? This would emulate the Omnistat where you can change the temp up/down and wait a second before it commits.
 
There is already a delay of 1 second. Also, the commands are actually queued so it should always end up setting it to the last value anyway. We will do some testing here to see if we can reproduce the issue.
 
Ok I have narrowed it down. It happens if you change the temp and change it again right around the one second mark. If you rapidly change the temp or wait around 2 seconds per change it works as expected.
 