Hi CollinR. "Does it work.." I have no idea. This is a new home. The contacts/motion/smoke and controller were all wired, but it does not appear they have been powered up. My plan was to wait until these guys finished the verification and then transition everything over to ELK. This way, I'd at least know I have a solid starting point.My money says Vista20p, A Vista 10 usually doesn't have a #8 and never has #18-20. The 15p has a #8 and supports 2 wire smokes between #8 & #9 but also does not have a #18-20. It appears this one has a #18-20.
I also find it somewhat strange how it's been wired aside from the previsouly mentioned EOL at the control they also were not trimmed back very well. But what I find the most strange is the zones wired in parallel, zones 3 or 4 (#12,13,14) and zones 7 or 8 (#18,19,20) all use 2k ohm when using zone doubling you should use 3k ohm for the first zone and 6.2k for the second.
Does it work properly?
Do you have to open all of the windows in a room to trip it or just a single window?
- Ed