An EOLR at the panel might have a very small value over no EOLR in the loop. But this value might be out-weighed by the risk of extra splice(s) at the panel. Plus just managing the extra 'stuff' at the panel adds to the risk (risk of physical or electrical damage). Yes there is a risk of damage when installed at the EOL, but these wires don't move much after installation....
Do folks place EOLR's at the panel on fire loops also? A bit different scenario as these are supervising an open loop. And an open type fault in a conductor/connection is MUCH more probable than a short type fault.
As Lou says, place all of the EOLR's at the EOL.
Do folks place EOLR's at the panel on fire loops also? A bit different scenario as these are supervising an open loop. And an open type fault in a conductor/connection is MUCH more probable than a short type fault.
As Lou says, place all of the EOLR's at the EOL.