that Elk application example is a little confusing. It says "It is recommended to connect the strobe to output 3, because it has a higher current rating which the strobe needs to operate properly." If I understand correctly, Output 3 is simply a relay, with dry contacts. The relay contacts might have a higher rating suitable for switching loads with higher current, but Elk seems to be missing a step in the instructions, by failing to mention options for providing power to the strobe. Am I missing something here?BraveSirRobbin said:FYI, HERE is the Elk application example of the strobe notification scenario I described above.
Are you having trouble hooking up your strobe?rexwilson said:that Elk application example is a little confusing. It says "It is recommended to connect the strobe to output 3, because it has a higher current rating which the strobe needs to operate properly." If I understand correctly, Output 3 is simply a relay, with dry contacts. The relay contacts might have a higher rating suitable for switching loads with higher current, but Elk seems to be missing a step in the instructions, by failing to mention options for providing power to the strobe. Am I missing something here?
The fire alarm is PTC protected from shorts on the power side, and on a 4 wire loop, would generate a trouble because the supervision relay would drop out. On a 2 wire circuit it's an alarm. No need to fuse and contradicts the operation of the circuit.BraveSirRobbin said:I think it comes down to one's comfort level. On my friend's and my install, I used the Elk power distribution modules as it made an easy job of fusing runs to motion sensors and glass breaks (power supply lines).
I would be hesitant on recommending fusing for smoke alarms, as I'm not sure of the code regarding this.
I'm sure there are a LOT of people though that do not fuse their powered sensors and have never had any problem as well. What you definitely do not want to do though is just blindly parallel your AUX power system all over the place without any sort of protection.![]()
Hmmm, for someone that complains about me showing polarity wrong on an EOL with the infinitesimal odds that a ground fault would happen in a metal door frame is making a statement like that?DELInstallations said:.... but fusing isn't generally needed and typically the wiring, if intact and not subject to compromise and installed properly, isn't going to develop a short circuit magically.
The point I was making is I would be far more worried about some "magical" thing happening to fault my main aux power supply over an EOL or contact closure type sensor fault.DELInstallations said:Nope. Not at all.
I pointed out a design error in a example you posted once...that's all. The schematic contradicted the installation instructions for the host panels and NBFAA best practices and provided reasons why it should not be placed where you called for it in your schematic.. I pointed out the error/oversight and where and why the EOLR should be installed in a specific location within the panel. EOLR's have no polarity, only a specific location, which is after the device on the common side of the loop.
I think you're confusing the real world examples of failures where I provided of sites we had old Logiplex systems that a ground fault developed on the wiring and tracking across the insides of a surface contact to an aluminum extrusion door frame combined with a steel buck on a security door. Same example of a mass of cables on a multi partitioned system that were stapled too tight under a romex staple.
The field wiring was not the issue, the issue was the conductors were damaged by the contractor that pushed all the slack into the bored holes without deburring the opening, and that was still just the last foot. The majority of issues I see on installed systems is not bad cabling, just bad installations of the cabling many times. While a short may develop, usually it's due to a different failure mode and not the cabling the majority of the times in the field.
It's part of the reason why I like having a graphical TDR at my disposal, such as when I've shown a contractor the distance and location +/- % of the staples they used on their cabling, wet/damp conductors or splice points that weren't supposed to exist.
Depends on the holder, but AGC and ATO would be the most common. You only need to fuse the output at .5A/12VDC at most...1A if you wanted to go higher.newalarm said:So on an exterior elk strobe, what fuse type and amp would your recommend?