The Installation Manual is very clear about not grounding the M1 Gold in numerous sections:
Page 4, Notes
"3. This terminal (formerly earth gnd) not used. Do not connect any neg terminals to ground."
Page 7, RS-485 Connector Note
"This terminal (formerly earth ground) is no longer used. Do not connect this or any neg. terminals to earth ground."
Page 11, Earth Grounding
"Tests have determined that the best results against lightning and transients are obtained by isolating the control from ground. Do NOT connect any of the terminals, especially the Neg. terminals to earth ground."
However, when I get to page 67, Appendix F - Regulatory Agency Statements, the instructions regarding auxiliary power supplies say: "Connect Negatives of both supplies together," i.e. jumper from the Elk M1 G ground on the RS-485 data bus to the negative on the auxiliary power supply.
The AC supply to my Altronix auxiliary power supply is grounded, but I'm not sure if the -12 VDC on the Altronix is grounded. Consequently, I'm not sure if I have ground passing through to the Elk -12 VDC.
Everything is operating fine. Do I need to worry about a possible grounding of the Elk -12 VDC through the Altronix PS?
[sharedmedia=gallery:images:767]
Page 4, Notes
"3. This terminal (formerly earth gnd) not used. Do not connect any neg terminals to ground."
Page 7, RS-485 Connector Note
"This terminal (formerly earth ground) is no longer used. Do not connect this or any neg. terminals to earth ground."
Page 11, Earth Grounding
"Tests have determined that the best results against lightning and transients are obtained by isolating the control from ground. Do NOT connect any of the terminals, especially the Neg. terminals to earth ground."
However, when I get to page 67, Appendix F - Regulatory Agency Statements, the instructions regarding auxiliary power supplies say: "Connect Negatives of both supplies together," i.e. jumper from the Elk M1 G ground on the RS-485 data bus to the negative on the auxiliary power supply.
The AC supply to my Altronix auxiliary power supply is grounded, but I'm not sure if the -12 VDC on the Altronix is grounded. Consequently, I'm not sure if I have ground passing through to the Elk -12 VDC.
Everything is operating fine. Do I need to worry about a possible grounding of the Elk -12 VDC through the Altronix PS?