HAI RC-80B only works with backlight?

theedudenator

Active Member
I just installed a HAI RC-80B.
Everything seems to work ok, heat kicks on, cool kicks on, fan only kicks on.

I woke up this morning to a cold house.

It seems that it work ONLY if the back light is ON!
So I can override the temp and the furnace will kick on.
But I have to keep pressing the overide button (or any other button) to keep the furnace running.

As soon as I let the backlight time out and shut off, it turns the furnace off.

From what I have read this is normally the opposite problem.
When I get home I am going to try to jumper the backlight to always be off, but figure I would post here first.
 
I just installed a HAI RC-80B.
Everything seems to work ok, heat kicks on, cool kicks on, fan only kicks on.

I woke up this morning to a cold house.

It seems that it work ONLY if the back light is ON!
So I can override the temp and the furnace will kick on.
But I have to keep pressing the overide button (or any other button) to keep the furnace running.

As soon as I let the backlight time out and shut off, it turns the furnace off.

From what I have read this is normally the opposite problem.

That is strange. Does your system have a common wire? If so, maybe it's become disconnected. If not, then perhaps your fan relay is going bad. I'm grasping at straws here.
 
I am not sure if I have a common

Red
White
Yellow
Green

I also have a blue wire that was connected to my old thermostat, I did not connect it to the new one.

My furnace worked fine with the old thermostat...

I wonder if my furnace is sensing a change in the load when the backlight kicks off, thus starting the shut down sequence?



That is strange. Does your system have a common wire? If so, maybe it's become disconnected. If not, then perhaps your fan relay is going bad. I'm grasping at straws here.
[/quote]
 
I have heard before that the backlight can cause issues on these thermostats. Usually a separate power supply is recommended, or turning it off might fix it as well. Keep us posted!
 
It sounds like it doesn't have a common if the unit only works with the backlight on. You'll have to check the heater to see which is the common on your unit.
 
It sounds like it doesn't have a common if the unit only works with the backlight on. You'll have to check the heater to see which is the common on your unit.


I changed the jumper on the unit to have the backlight on all the time.
Now it works fine.

I looked at my furnace and the manual. I am not seeing a "common"

W1 W2 Y G RH

W1 and W2 are jumpered together at the furnace.

So I don't have a common on my furnace then?
 
Looking at the wiring for my furnace I do not have a common connection.

So now I need to run a separate power source?


I changed the jumper on the unit to have the backlight on all the time.
Now it works fine.

I looked at my furnace and the manual. I am not seeing a "common"

W1 W2 Y G RH

W1 and W2 are jumpered together at the furnace.

So I don't have a common on my furnace then?
[/quote]
 
Initially the same thermostat would cause problems with HVAC motherboard and the thermostat itself would act up.

I had to add an additional power source for mine. Its been a couple of years now and all is well.
 