I got sidetracked from the reversing relay testing when I found a new path from one end of the house to the other. This had been delaying me from hooking the thermostat for one. It will also let me tie in the sprinker and a few other things.
I got everything connected (the HAI RC80B to the M1XSP), but on the keypads if I go to temperature, it says 'Not enabled'. If I log in via the M1XEP, and go to the thermostats page (I set up Thermostat 1 as Kitchen via ElkRP, which shows up properly), it says 'Unit Not Responding'.
The light on the serial expander seems to blink once every half-second, but on every other blink it adds another (a flicker).
I confirmed communications mode is set to 0 (setting 01) so the HAI expects 300 baud, RS-232. The unit number in the thermostat is set to 1, and the address setting is down, up up up (meaning it is set to unit 1).
The baud jumpers on the M1XSP are all down (000), and S5 is on, S5 is off, S7 is on, s* is off. JP3 is set to 232.
JP1, JP2 are cleared.
JP5 is set.
The XSP enrolls properly (if I go to edit though the XSP shows up as address 14, which I did not quite follow, not sure if that is an indication of anything). Currently it is a keypad, the M1XSP then the terminator in the data bus hub.
I have 4-conductor wire connected to the 4 wire comm harness for the HAI, which is tied to the XSP via the supplied db9 connector. Only variation there is the silver goes to yellow, and the blue goes to green, but this should not be the issue (I don't think) since it is just the differnt coloring schemes, which do match on both ends.
I have the M1XSP connected to a data bus expander. I'm using rj45 on one end for the data bus hub, and the following to the XSP:
brown - +12x
orange/green - A
orange stripe, green stripe - b
brown stripe - neg.
I checked on the elk boards and went through suggestions there as well.
I've checked the log using ElkRP and there are no unusual items there either.
Anything anyone can think I might have missed before I try tech support?
I got everything connected (the HAI RC80B to the M1XSP), but on the keypads if I go to temperature, it says 'Not enabled'. If I log in via the M1XEP, and go to the thermostats page (I set up Thermostat 1 as Kitchen via ElkRP, which shows up properly), it says 'Unit Not Responding'.
The light on the serial expander seems to blink once every half-second, but on every other blink it adds another (a flicker).
I confirmed communications mode is set to 0 (setting 01) so the HAI expects 300 baud, RS-232. The unit number in the thermostat is set to 1, and the address setting is down, up up up (meaning it is set to unit 1).
The baud jumpers on the M1XSP are all down (000), and S5 is on, S5 is off, S7 is on, s* is off. JP3 is set to 232.
JP1, JP2 are cleared.
JP5 is set.
The XSP enrolls properly (if I go to edit though the XSP shows up as address 14, which I did not quite follow, not sure if that is an indication of anything). Currently it is a keypad, the M1XSP then the terminator in the data bus hub.
I have 4-conductor wire connected to the 4 wire comm harness for the HAI, which is tied to the XSP via the supplied db9 connector. Only variation there is the silver goes to yellow, and the blue goes to green, but this should not be the issue (I don't think) since it is just the differnt coloring schemes, which do match on both ends.
I have the M1XSP connected to a data bus expander. I'm using rj45 on one end for the data bus hub, and the following to the XSP:
brown - +12x
orange/green - A
orange stripe, green stripe - b
brown stripe - neg.
I checked on the elk boards and went through suggestions there as well.
I've checked the log using ElkRP and there are no unusual items there either.
Anything anyone can think I might have missed before I try tech support?