apostolakisl
Senior Member
I ran a test using the LED previously described. I connected it directly across the zone terminals for a zone on an M1XIN zone expander. The zone is defined as normally open, non-alarm.
Before connecting the LED, Elk RP showed...
Status: Normal
State: Open (+)
Volts: 14.0
After connecting the LED, Elk RP showed...
Status: Violated
State: EOLR (=)
Volts: 5.2
I left the LED connected for a couple of minutes. It didn't heat up at all that I could tell by touch.
If I were to put this into use, there would be a N/O relay involved. The LED would be wired in series with the relay. So, I would wire one of the M1XIN zone's terminals to one contact on the relay. The other relay contact would be wired to one of the LED leads. The other LED lead would be wired to the other M1XIN zone's terminals (keeping in mind the polarity of the LED).
So is Elk RP trying to tell me this is okay? Why is it showing the state as "EOLR (=)" when I have the zone defined as normally open? Is it because the LED isn't letting all the voltage thru like a simple contact closure would, so it thinks there is an EOLR present?
Thanks,
Ira
I just looked at your original question and realized we weren't exactly answering it.
Since elk posted "eolr (=)" with 5.2 volts, Elk is interpreting that as within its range of eolr protected zones. Probably somewhere in the specs section of the manual it will tell you what the exact range is that defines how elk interprets the value. If 5.2 is right on the cusp of being defined as "short", then you probably will want to tweak things with other resistors, but I bet it isn't.
Basically, elk has three ways it can interpret the status at each zone: short, open, eolr. The status screen in elk rp reports both the raw data (volts) and what it thinks of that data (short, open, eolr).
How elk responds to those three states is a different matter all together and is defined by you when you setup the zone. If the zone previously worked like you wanted as a nc zone, then adding the led means you change it to eol supervised. Elk programs will now respond to the +/-5.2 v the same as the responded before to +/-13.8v.