I am bench testing my unit and still figuring out things.
I have a magnetic contact that can be NO or NC. I wired it for NO. I installed a EOLR in parralel, as the ELK wiring diagram indicates.
I programmed the Control to: 03 = buglar perimeter instant.
Then If i do either:
3= eol supervised on short
or
4= eol supervised on open
I get a trouble signal when the magnetic contact is separated (door being opened), without the alarm being armed. I did repeat the test with wiring the contact as NC (I just thought of that and will try this evening.)
I wired a motion on a separate zone, supervised, NC with the EOLR in series and the Control set to 3= eol supervised on short and this work perfectly. no trouble when the contact is open (motion sensor senses motion) in unarmed mode, if i short the circuit, i get trouble. When armed, the alarm goes off.
I apologize if this has been explained in past post, but i did a search and could not find anything.
Thank you in advance.
I have a magnetic contact that can be NO or NC. I wired it for NO. I installed a EOLR in parralel, as the ELK wiring diagram indicates.
I programmed the Control to: 03 = buglar perimeter instant.
Then If i do either:
3= eol supervised on short
or
4= eol supervised on open
I get a trouble signal when the magnetic contact is separated (door being opened), without the alarm being armed. I did repeat the test with wiring the contact as NC (I just thought of that and will try this evening.)
I wired a motion on a separate zone, supervised, NC with the EOLR in series and the Control set to 3= eol supervised on short and this work perfectly. no trouble when the contact is open (motion sensor senses motion) in unarmed mode, if i short the circuit, i get trouble. When armed, the alarm goes off.
I apologize if this has been explained in past post, but i did a search and could not find anything.
Thank you in advance.