Thanks... Just to be sure, you mean the 3-way 'slaves', right? Or do you mean the scene switches? As you mentioned these will require 12 wires (since I have access to the 2nd floor from the attic and the 1st floor from the basement, I should be able to run additional cat5 myself if need be.
The slave switches for 3-way (and 4, 5 way) do not count toward the 31-device branch limit.
The scene switches DO count towards the device limit. They require only 2 LV conductors. (plus 120v hot, neutral, and ground). They work through the lighting controller to generate scenes.
The 4 device aux switches are dry-contact only, so they are not on the communication bus, do not count towards the device total. They can essentially act as slave switches to 4 regular ALC switches (or they can act as 8 momentary SPDT switches, I assume, so they could be used to command an automation panel like the Elk to fire scenes). And, I understand they can only fit in a single-gang box.
Others will proofread and correct my analysis, I am sure!
Ack! Somehow during my planning stages I missed that the scene switches require HV! I thought they were LV only.. There goes my plan of attaching an LV gang to the HV gang, running my CAT5 there and putting in a scene switch in that extra plate...
Ok, and just to verify - I can piggy back off adjacent switches hot and neutral right? I don't need an extra line?
Damn! My plans are foiled.. Good thing they haven't even started to pour the basement yet.