I have an Elk M1G and I just ordered a couple of SPY4 PIRs to play with. I'm using them for automation and just to track movement through hallways.
So, according to Visonic's web site, they state the following for power requirements for the SPY4:
OK, I don't quite understand what "Alarm Output" means. Does that mean that whenever the PIR detects movement it may peak up to 100mA usage?
I am thinking about buying an ELK-PD9 (maybe the HC) to provide power to a number of PIR sensors. The PD9 supplies a maximum of 250ma to each output. Does that mean I could only connect 2 of the SPY4 PIRs to each PD9 output? Or do I use the "Standby Current Drain" value to calculate the number of PIRs connected to each PD9 output?
So, according to Visonic's web site, they state the following for power requirements for the SPY4:
- Standby Current Drain: 12.5mA at 12VDC
- Alarm Output: Up to 100ma
OK, I don't quite understand what "Alarm Output" means. Does that mean that whenever the PIR detects movement it may peak up to 100mA usage?
I am thinking about buying an ELK-PD9 (maybe the HC) to provide power to a number of PIR sensors. The PD9 supplies a maximum of 250ma to each output. Does that mean I could only connect 2 of the SPY4 PIRs to each PD9 output? Or do I use the "Standby Current Drain" value to calculate the number of PIRs connected to each PD9 output?