DELInstallations said:(I laugh about the biopharma place near your house, they're supposed to go to IP cameras on the goosenecks that just had air terminals installed on them).
That could make for some exciting video!
DELInstallations said:(I laugh about the biopharma place near your house, they're supposed to go to IP cameras on the goosenecks that just had air terminals installed on them).
LarrylLix said:First is it best to isolate the ditek ground wire from it's metal enclosure so that the enclosure doesn't become energized in a lightning strike?
Think about voltages differences. Do you want your circuits to be at different voltages where the tendency is to discharge via your electronics through to the metal cabinet they are mounted on?
Think about the humans. Do you want somebody leaning against the cabinet to have a voltage on the cabinet that isn't on their feet or other hand.
Connect all together inside the cabinet to the cabinet (usually a stud passthrough the metal cabinet) and then connect cabinet (other end of stud) to garage panel ground. Reduce any differences in voltage on items that are in close proximity, generally.
RAL said:This is one of those cases where you should bite the bullet and do it right. You've spent the money to buy the surge arrestor, so why take a shortcut and potentially sacrifice some of the protection it is supposed to provide? The way I see it, you really won't have an extra splice if you place it where the cable enters the house. You need to run the cable through the Ditek's terminals no matter where you place it. Well, maybe you save something if you place it outside in the LB, where there already is a splice, as that would do double duty there. But if you place it just inside the house or in the M1's can, then the count is the same.
Also, I'd want to avoid putting anything that will experience a potentially high voltage during a surge inside the can with the M1, or in my electrical panel. Keep them separated, if possible.
Neurorad said:If you install a new ground rod at your home, I believe it must be bonded to the existing ground rod.
But I have no experience with isolated grounds, and this Ditek. Maybe it's Kosher? Is this metal cabinet connected to anything else?
DELInstallations said:That's what I get after posting while having a cold one....
You're a better man than me Mike. The supplementary rods weren't really necessary in this case and you could've bonded to the existing ones installed for the service.
Bonding the enclosure won't hurt, but it's not necessary either. The cabinet doesn't have the real possibility to carry current unless you have a LV ground fault.
And yes, the M1 is supposed to be isolated (no EG necessary) as you already posted. Usually most alarm panels perform best with no EG in the case of a surge (but then again, the surge typically feeds in via telephone and out via the transformer/neutral).