d.dennerline said:
The M1DBH documentation does describe how two DBHs can be connected together using a cross-over cable. You would use the garage RJ-45 for cross-over cable. At the same time, the M1DBHR (different product) seems to indicate that you cannot remote a second DBHR. I don't know if M1DB has same limitation.
Without M1DBH, ElkM1 provides two seperate loops via data A and B. I wonder how the M1DBH patches both the A and B data buses together.
I think you might want to obtain support from Elk (through your dealer) and draw out your network picture. There are so many variables involved.I could not find a application note how to hook up a secondary building using two DBHs. There is a limit on the length of RS-485 bus.
Maybe it might be better to use *one* M1DBHR for entire system instead of two M1DBH as the DBHR seems to do a better job at handling separate isolated branches with multiple devices on each branch.
The OP does not need any special cabling or considerations if 2 DBH's are connected and wired in parallel at the control. The only item that requires consideration is the removal of the termination jumper at the panel (JP3). There is no need or requirement to negate a second DBH or require one for this installation. The only reason why one would be negated or installed would be to facilitate easier field connections for bus devices and in technicality, he could have 8 or 10 hubs installed with no ill consequences. Without getting into specifics DBHR's are a different animal, but you can also have much more than a single one installed as long as the terminating jumpers are paid attention to. There's reasons why they state to NOT install them in the field, but that is a different discussion altogether.
The DBH does not provide any special connections or feed throughs when cascading from another DBH...all you are doing by connecting a crossover cable is taking the cables that would be "out" on the RJ45 and moving them to an "in" position on the secondary DBH.
At this point, based on the issues described, I'd start investigating the cable that connects the garage branch and pinouts as appropriate. Possibly take the direct burial, restrip and reterminate, then run that bus, terminated in the field, with no devices and then move a single device at a time to see when the errors start to occur.
As an aside, what is the total overall run of all attached devices? Remember, the M1 can only handle 4K total length, and by using a Cat X cable, that length is halved.
Wiring multiple busses and devices on an M1 isn't rocket science, there's really only 2 ways to do it and no real network topology or variables. You either bring 2 data wires to the device and feed the next device downstream or you don't (and terminate the bus at that device). The DBH just forces your hand to feed/return the data bus and install the 120 ohm resistor in that little RJ at the hub. No different than if you ran enough conductors, tied through, and installed your own 120 ohm resistor at the last data pair.